    Haier AD28NAAMBEA fault but no code



    Chaps,

    looking at a Haier ducted split which has been playing up for some time. The previous company diagnosed a faulty compressor but on running it seems fine although the unit stops after a minute of operation on either heating or cooling

    There is a hard wired controller but no faults show. The indoor board has flashing lights but seem more random.

    One thing I did notice that the outdoor ambient sensor had been chopped and the wired taped together, the actual sensor was missing

    I assume the first thing would be to replace the sensor but wonder if anyone has any ideas?

    Richard
    Last edited by r.bartlett; 16-04-2016 at 04:26 PM.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Haier AD28NAAMBEA fault but no code

    when it stops is it comp only or cond fan? - might be worth sticking a resitance box or a fixed resistor to trick it to think the ambient is 28deg- which it prob is in your hood, would have thought that the system wouldnt run at all if senssor is linked out

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Haier AD28NAAMBEA fault but no code

    condensate hi limit float switch?

  4. #4
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Haier AD28NAAMBEA fault but no code

    Found this install manual if of any use, has some fault code info:

    http://www.google.co.uk/url?sa=t&rct...pjvia7ifMPcnBw

    and another one here which I'm not sure applies to your model but has all sorts of service info inc. probe resistances:
    http://www.google.co.uk/url?sa=t&rct...uZwsYp9tyPIsIA

    Other than that not really messed about with Haier.

    Heard someone describe them as worse than LG if you could confirm? :-)

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  5. #5
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Haier AD28NAAMBEA fault but no code

    Thanks chaps, no fault codes just runs for one minute off 5 ..

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Haier AD28NAAMBEA fault but no code

    Don't suppose it's clever enough to consider frost protection on the evap?

  7. #7
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Haier AD28NAAMBEA fault but no code

    Quote Originally Posted by frank View Post
    Don't suppose it's clever enough to consider frost protection on the evap?
    It was 25 deg C so unlikely but it was to the second which means the pcb was timing an error but not reporting it.....:-)