    Compressor Terminal Arcing



    Hi Guys , i have a brand new comp that has failed its earth resistance test. I pulled the terminal plate and found arcing between a terminal post and the plate.
    Has any one seen anything similar or know how this may of occurred ?
    Attachment 14076Attachment 14075Attachment 14074



  2. #2
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Compressor Terminal Arcing

    Your pictures won't load.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  3. #3
    Join Date
    Dec 2009
    Location
    New Zealand
    Age
    50
    Posts
    73
    Rep Power
    16

    Re: Compressor Terminal Arcing

    Pics attached again hopefully.
    Attached Images Attached Images

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Compressor Terminal Arcing

    As a guess, moisture or lightning. I'm sure others will have some better ideas!
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Compressor Terminal Arcing

    Hi normally when this happens when everything tight
    (1)the insulator in the terminal plate is tracking and faulty
    (2)when the terminal plate is bolted down the crimp is very close and arcs

  6. #6
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Compressor Terminal Arcing

    Hi Andy

    I've never seen anything like that before.

    I am thinking along the same lines as monkey spanner, moisture in the terminal box.

    Moisture in the terminal box might have started it, but once you get the carbonation (if that is the correct word) residue across the insulating agent between the terminal and the body, it creates a conducting path that makes the problem worse.

    the initial problem could be moisture, or an abnormally high starting current, or a combination.

    As a solution:

    Clean the terminals and put heat shrink tubing over the terminals to cover them all the way down to the insulator.

    http://www.transnet.co.nz/shop/Heats...nk+Tubing.html
    -Cheers-

    Tycho

  7. #7
    Join Date
    Dec 2009
    Location
    New Zealand
    Age
    50
    Posts
    73
    Rep Power
    16

    Re: Compressor Terminal Arcing

    Hi All , thank you for all your replies . Just one thing to clarify , the arcing is on the internal side of plate so im sure moisture should not be an issue. Will wait to here from manufacturer about what they think.
    Thanks again.

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor Terminal Arcing

    Is this arcing due to someone testing when the compressor was under a vacuum?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Compressor Terminal Arcing

    the lug on the terminal isnt as bent as the other 2

  10. #10
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Compressor Terminal Arcing

    Voltage drop on that phase when under load. The other 2 connections are showing signs of excess heat.
    Last edited by mikeref; 08-04-2016 at 08:45 AM.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  11. #11
    Join Date
    Dec 2009
    Location
    New Zealand
    Age
    50
    Posts
    73
    Rep Power
    16

    Re: Compressor Terminal Arcing

    Hi all , its been established that the damage to terminal block was caused by testing insulation resistance while the comp was under vacuum.
    Thanks for all your comments.

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor Terminal Arcing

    Thank you for providing the update.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Compressor Terminal Arcing

    Quote Originally Posted by AndyHX View Post
    Hi all , its been established that the damage to terminal block was caused by testing insulation resistance while the comp was under vacuum.
    Thanks for all your comments.
    Andy you are living proof as to what happens whereas many have disputed that in a vacuum this could happen.
    Well done and as Brian says Thanks for the update.
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  14. #14
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Compressor Terminal Arcing

    Hi Andy.
    again from others , thanks for reporting back on actual cause of problems.
    Out of interest what level of meg testing was actually done , voltage value etc., that created the problem, was it an electronic meggar type test instrument, or an electronic multi meter.
    regards

  15. #15
    Join Date
    Dec 2009
    Location
    New Zealand
    Age
    50
    Posts
    73
    Rep Power
    16

    Re: Compressor Terminal Arcing

    Here is an article on resistance of a vacuum. Interesting stuff.

    Magoo, 500v megger.

    http://qdl.scs-inc.us/2ndParty/Pages/8819.html

  16. #16
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Compressor Terminal Arcing

    Hi Andy
    This type of fault happens more than you think, as ive seen several instances of this whilst doing compressor warranty work. I'm convinced this is a situation which happens when different trades are involved on the same installation, and a lack of inter trade knowledge can cause system issues such as this.
    playing devils advocate lets see what happens.
    Main Contractor (A) REFRIGERATION , installs the fridge system and pipe work, SUB contractor (B) ELECTRICAL, installs the Control panel and the associated wiring. The fridge installation is now pressure tested etc, and then the system is evacuated. The electrical installation is now finished . The electrical system is now check and metered for integrity, continuity and insulation before being signed off. Does the electrician Know that the system is under a deep vacuum? does he know that meggering a semi or hermetic compressor under a deep vacuum can damage the compressor motor ? or simply manually pushing a compressor relay in, to kick the compressor over whilst its under a vac can also damage the motor. Many electricians ive spoken too have no idea that in the fridge trade that testing or running a compressor under a vacuum is a total NO NO.
    The Refrigeration engineer should know this but the electrician ?.
    I had a situation recently where I went to look at a new coldroom which was nearing completion. The Electronic expansion valve hadn't been set up correctly. While I was on site the sub contract electrician was fitting the Flourescent lamps inside the cold room. The electrician had made a fantastic neat installation of the lamps inside the room. Their was one large evaporator at one end of the room ,the lights had been installed in pairs every 1.5 metres down the long room. Unfortunately he had mounted them in line with the evaporator across the ceiling, which would totally destroy the Coanda Effect of the air being blown down the room, which would have caused bad air circulation and hot spots in the room. When I told him what effect fitting the lamps in that configuration would have on the operation of the room he was angry that no one had explained this to him before, I explained it was up to him if he left them as they were or if he changed them as I had no authority on the site, but he could see the problem and turned all the lamps 90 degrees so the air flow was no longer impeded. He later thanked me for the advice, and said how was he expected to know that !!!! Good question. This is the blame game, or get out of jail free card.

  17. #17
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Compressor Terminal Arcing

    Glenn, I totally agree with you but have one question,
    Shouldn't there be a position of supervising? One skilled person that knows what anyone's else's job?
    What to do and when?

    Seems strange to me as I have an electric license and do all the controls and electricity myself. [up to a certain cold room size]

  18. #18
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: Compressor Terminal Arcing

    I had a similar issue where I was called to a site that had lost three comps on a new install three decent engineers had installed comp very good install engineer with a torr gauge but sometimes he was a bit keen to leave on a Friday anyway it was again diagnosed another comp blown history as follows
    Installed may 2002 r404a chiller room 6mx 3m room medium use correct size kit
    On install after 24 hrs blew trips engineer went to site comp gone comp fitted
    Two days after comp install trip blows again engineer visit new comp needed
    Four days after that trip blew engineer goes to site comp blown
    Then I got the call to fit new comp and find out what's going on so called install engineer who advised room on wrong breaker a type b and he advised on site sparky to fit a c so any way I role up with a very upset customer so fit a comp change a breaker no debris in system ran system all pressures temp oil levels good until it pumped down and it pumped into a vacumn so I set it up and ran and done nothing else so I called the three previous engineers who fitted comps and asked was comps dirty inside or smelly and all three said no .....now right or wrong I reckon the room was blowing trip because wrong breaker to small and wrong breaker I believe all units where pumped into a vacumn and when insulation tested which then fried comp all three of um ...... that room still running on same comp now which is a bit rich but averages a comp every 4 years so not to bad now anyway just proves bit of time cup of tea bit of thought and all is cure able what I am really saying is Glenn I agree with you ta charlie

  19. #19
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Compressor Terminal Arcing

    Your right Charlie,when you change any compressor find out why the old one failed,and on semi hermetically always change the contactor/overload and starting kits on single phase oh and always monitor while drinking a few good cups of tea and hobnobs!

  20. #20
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Compressor Terminal Arcing

    Thanks Charlie
    Hi Chemi Yes your right there should be someone who is an all rounder supervising the site, but due to costs many large contracts are subbed out to contractors for electrical and pipe work, and the only time anyone with any real fridge knowledge gets to site , is when the commissioning engineer arrives and he then has to sort out the mess left by others.
    One large industrial contractor regularly used to call me out during the commissioning stage complaining that the Danfoss valves in the system would not work or were letting bye etc. The pipe work contractor uses a grinder to cut the steel pipe , and on one site there was even shingle (stones) inside the valves which had come via the pipe work from the site walkways and carpark. Rule 1 in refrigeration CLEANLINESS Rule 2 Cleanliness
    .

  21. #21
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Compressor Terminal Arcing

    Sadly pricing is the downfall ,and others have to correct the mess a now retired top engineer used to call them cowboys they ride into town shoot the sheriff then ride off into the sunset with the loot,great products like danfoss tried tested and respected in the industry get blamed for others incompetence !

  22. #22
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    451
    Rep Power
    17

    Re: Compressor Terminal Arcing

    Interesting