    GTH (KW) & GTSH (kw) Sizing



    Hi,

    I am quoting a project that has been engineered, with the Air conditioning specs I have been given a table with each air con design. There are two columns GTH and GTSH(KW). This is the first time have I quoted jobs like this, so I just want to make sure that I am on the right track. I assume that the GTH is the Air conditioning size in KW, is this correct or is there more to it?

    Kind regards



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: GTH (KW) & GTSH (kw) Sizing

    Try

    GTH Grand total heat
    GTSH Grand total sensible heat

    And, welcome to the forum.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: GTH (KW) & GTSH (kw) Sizing

    The ratio between each is the SHR sensible heat ratio, difference between a good design and a cheap design. be carefull, have a safety factor in your favour, particually in Australia. Ambient conditions can go from dry to humid in a matter of hours.
    What part of australia are quoting for. ? Check the average weather conditions for a several year period to get a grasp on averages.

  4. #4
    Join Date
    Apr 2016
    Location
    Australia
    Posts
    9
    Rep Power
    0

    Re: GTH (KW) & GTSH (kw) Sizing

    I am quoting for QLD. So the total of the two is just an extra heat load. This then needs to be added onto the heat load for the m2 of the room size?

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: GTH (KW) & GTSH (kw) Sizing

    Hi
    in a word NO. !!!!!!
    Queensland is HOT and steamy on occassions, with the odd cyclone as a test.
    Start again, grand total heat is what the cooling system will max supply, which includes sensible and latent cooling. sensible being the real effective cooling that clients can feel, as a body . Latent is the removal of moisture with no effective temperature change , basically ripping moisture out of the enclosure space.
    Selecting equipement for a single office space or a high rise building is critical, the SHR is very important

  6. #6
    Join Date
    Apr 2016
    Location
    Australia
    Posts
    9
    Rep Power
    0

    Re: GTH (KW) & GTSH (kw) Sizing

    Yes that all makes sense now. Sorry I got a bit confused. For a similar job I am sizing for a school For a domestic application I have been shown to use 150w per m2. for this school I have used this plus 3660w for 30 kids. I have worked this out form my text book. I have then added another 10% safety.

    eg.

    65m2x150=9750w Plus 3360 = 13410 + 10% =14751w.