    Large electric motor connections



    With the connection of a large electric motor, let's say 100kW & above, should you revisit terminal connections after a few days of running?
    Recently had a motor fail because of possible loose connection after running for several weeks.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Large electric motor connections

    Hi Ranger.
    We still have check motor terminals as an option listed on most of our check sheets.
    However I cannot remember the last time I did it or it was a problem.
    My question would be as to what value they were torqued up to, in the first place?
    Also where they the fork copper strands clamped between 2 plates. Or the preferable crimped spade / eyelet type.
    It is a rare fault all the same.
    I will try and see what advise I have stored Manufacturer wise and get back to you.
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Large electric motor connections

    Thanks Grizzly,
    It was crimped eyelet type I think on 465 kw motor.
    Never heard of it & usually rely on electricians (who in this case very experienced).
    expertise, although makes sense

  4. #4
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Large electric motor connections

    There are set torques to be used on the motor terminals, and as long as it's done with crimped eyelets and properly torqued I see no reason for it to have to be re-checked.

    During commissioning I check the terminals to see if the electricians have marked each of the terminal connections with a permanent marker, I have found that electricians who do that, torques them up and marks them one by one to make sure it's all done properly.

    During compressor service or service checkups I check the cable/wires inside the terminal box for wear and tear, insulation dry and cracking, insulation chafing because of vibration and also a quick check for discoloration on any of the terminals (indicates uneven load on the phases)
    -Cheers-

    Tycho

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Large electric motor connections

    hi
    it is better to use 2 nut to luck it.

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Large electric motor connections

    I think motor repairer at fault to a certain degree, as not doing nuts up tight enough.
    We maybe at fault not checking them.
    Motor was bench test run & given tick of approval, motor put on truck for 20km.
    Install, run for 3 weeks & tails blow off, live & learn.

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Large electric motor connections

    Hi, Ranger1

    usually, electrical connection is made by some skilled electrician and electrical supervisor...
    as I remeber never did any re-check i.e. never ever heard about similar problem ...

    for sure can be a problem if job was not done properly from beginning ... but you know sh... happens ....

    life is full of unpredictable events ... it is not possible to control all at all times ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Large electric motor connections

    Quote Originally Posted by Josip View Post
    Hi, Ranger1

    usually, electrical connection is made by some skilled electrician and electrical supervisor...
    as I remeber never did any re-check i.e. never ever heard about similar problem ...

    for sure can be a problem if job was not done properly from beginning ... but you know sh... happens ....

    life is full of unpredictable events ... it is not possible to control all at all times ...


    Best regards, Josip
    Thanks Josip,
    For me this scenario will not happen again.
    On both occasions used experienced industrial electrician.

    After awhile to many things to tick off to prevent failure or problem, but you can only try.

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Large electric motor connections

    Hi Ranger
    had a coil tail overheat due to be not being tight after a rewind, was noted after 6 months with connection plate overheated/ cooked around the stud. The feild wiring terminations fine. Re crimped with new lug, not alot cable to work with though.

  10. #10
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Large electric motor connections

    Quote Originally Posted by RANGER1 View Post
    With the connection of a large electric motor, let's say 100kW & above, should you revisit terminal connections after a few days of running?
    Recently had a motor fail because of possible loose connection after running for several weeks.
    HI
    We had a similar issue, but the problem turned out to be inside the motor , the connection to the lugs on the inside ,under the connection plate, were loose ,luckily the vsd stopped the motor in time to fix it.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!