    Booster compressor Relief valve



    Tanks watching this question.

    First I'm sorry my English uncomfortable.

    I saw that "The refrigerant relief valve must be connected in the discharge line between the
    compressor and the shut-off valve." as Fuller rotary compressor.

    In my common sense, Relief valve can not working flow low pressure to high pressure side.

    How can work that relief valve?

    Or Has some different suitable relief valve?

    Newbie Grateful waiting for your answer.

    Booster_Relief_valve.png



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Booster compressor Relief valve

    Hoon,
    I think it is OK, as CHECK ARROWS on pipework indicate suction & discharge.
    The pressure readings on suction & discharge is incorrect.
    Suction normally 0psi or vacuum & discharge no higher than 45psi.
    On picture suction is 250psi & discharge 75psi.
    Relief valve is in correct position, but should now be special type balanced port or down stream pressure not effecting relief valve set point pressure or relieving pressure.

  3. #3
    Join Date
    Mar 2016
    Location
    USA
    Posts
    4
    Rep Power
    0

    Re: Booster compressor Relief valve

    Ranger, I Really appreciate it.
    Yes, as you said, when that machine running, It usually suction side is 0 psi.
    I have got some wrong inform.

  4. #4
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    867
    Rep Power
    26

    Re: Booster compressor Relief valve

    The drawing is labeled with the pressures reversed as Ranger noticed.
    However the relief valve function is a bit different here.
    As I remember the maximum pressure differential is 45 psi across the machine.
    In order to prevent a high pressure differential the relief valve is installed. It does not need, nor should it be, the type which references ambient pressures.
    The differential pressure is the only thing we are concerned with in this case.

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Booster compressor Relief valve

    Quote Originally Posted by NH3LVR View Post
    The drawing is labeled with the pressures reversed as Ranger noticed.
    However the relief valve function is a bit different here.
    As I remember the maximum pressure differential is 45 psi across the machine.
    In order to prevent a high pressure differential the relief valve is installed. It does not need, nor should it be, the type which references ambient pressures.
    The differential pressure is the only thing we are concerned with in this case.
    Not sure I agree, will get back to you on that one.

  6. #6
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    867
    Rep Power
    26

    Re: Booster compressor Relief valve

    Always up for a technical debate! Us retired guys are like that.
    Think the internal relief on a Vilter compressor.
    Hope all goes well down under!

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Booster compressor Relief valve

    I have found that generally the non return / check valve creates most issues with Fuller boosters if not removed and serviced regularly. Just a thought.

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Booster compressor Relief valve

    NH3LVR,
    Checked Fuller manual & come up with the following.

    Differential pressure across machine maximum 45psi
    Relief valve from discharge to suction 75psi

    If differential pressure, high pressure or high interstage pressure switch failed or was started with discharge valve restricted or closed, then relief might work.

    If compressor isolated it has no relief valve to protect it against over pressure.

    No real description of relief valve function, but states if differential exceeds 45psi problems will occur.

    Relief valve would probably never go off until you potentially damage blades.

    If machine was isolated it would not protect compressor or jacketing as it returns downstream of suction stop valve.

    A relief that vents back into system that is protecting something at a predetermined pressure should be not downstream pressure affected in any case otherwise setting is a moving target.

    These machines were built in a era where they were monitored very regularly by operator checking plant pressures & lubricator oil levels.

    As for Vilter internal relief it's no better or effective than the Fuller set up, but what can you do except make sure all safety switches are set correctly & work!