Results 1 to 6 of 6
  1. #1
    Join Date
    Jun 2008
    Location
    U.A.E
    Posts
    5
    Rep Power
    0

    Grooved flexible couplings (Grinnell & Victaulic) allowed in R134a piping?



    I have the following question:
    Are grooved flexible couplings (Grinnell & Victaulic) allowed in R134a piping as per ASHRAE-15 & ASME B31.5?
    I do cannot find any particular exclusions of these type of piping joints in these standards.

    Anyone has the answer?
    Cheers



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Grooved flexible couplings (Grinnell & Victaulic) allowed in R134a piping?

    I cannot find any Victaulic documents relating to its use with refrigerant and to be honest I wouldn't use it either. Goes against all recognised safe jointing methods I think.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2008
    Location
    U.A.E
    Posts
    5
    Rep Power
    0

    Re: Grooved flexible couplings (Grinnell & Victaulic) allowed in R134a piping?

    Thanks Brian. In this case it would be mounted in the Refrigerant relief vent header.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Grooved flexible couplings (Grinnell & Victaulic) allowed in R134a piping?


  5. #5
    Join Date
    Jun 2008
    Location
    U.A.E
    Posts
    5
    Rep Power
    0

    Re: Grooved flexible couplings (Grinnell & Victaulic) allowed in R134a piping?

    Thanks Chemi-cool,

    I have been reviewing this, but could find only:

    518 SLEEVE COUPLED AND OTHER NOVELOR PATENTED JOINTSCoupling type, mechanical gland type, and otherpatented or novel type joints may be used providedadequate provisions are made to prevent separation ofthe joints and provided a prototype joint has beensubjected to performance tests to determine the safetyof the joint under simulated service conditions. Whenvibration, fatigue, cyclic conditions. low temperature,thermal expansion, or hydraulic shock are anticipated,the applicable conditions shall be incorporated in thetests.

    I cannot draw a clear conclusion from this clause.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Grooved flexible couplings (Grinnell & Victaulic) allowed in R134a piping?

    If you have doubts, dont use it.