    Suction filter installed in the wrong direction.



    What would happen theoretically if you installed the suction filter with the arrow point toward the evaporator? Also I am interested in any examples from the field i.e. installaties that work fine or not with the filter in the wrong direction and the consequences.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Suction filter installed in the wrong direction.

    The main issue is there is no felt pad on the inlet of the drier to catch small bits and pieces that may break off the drier core when the flow is in the wrong direction. Flow wise there would not be any difference.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Suction filter installed in the wrong direction.

    Suction filters are good for new units and will protect suction accumulator and compressor if unit is not clean.

    After some running time they should be removed as they will not do anything.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Suction filter installed in the wrong direction.

    if left in the system then they can knacker the pot

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Suction filter installed in the wrong direction.

    What ever direction they will trap junk in system , but remove them after clean up period. If a flared add in remove it, if a cartridge type remove cartridge. The cartrige type add suction pressure drop and reduced performance on a good day, had situation that felt cartridges collapsed and seriously stuffed things up on a large cold store and of course in summer period

  6. #6
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Suction filter installed in the wrong direction.

    By fitting the filter in the wrong flow direction will reduce its filtration capacity , and if the system is dirty will cause high PD's very quickly