    mitsubishi pury



    I have 2 Mitsubishi pury p 400`s connected together freezing up. Master unit runs okay but pipework freezes up, slave unit the accumulator is a block of ice and pipework freezes up.
    Have tried added refrigerant but compressor on slave locks up with liquid.
    Any ideas



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: mitsubishi pury

    You should recover all refrigerant from both units and weigh in correct amount. Than you can proceed with your troubleshooting further!

  3. #3
    Join Date
    Feb 2012
    Location
    england
    Posts
    14
    Rep Power
    0

    Re: mitsubishi pury

    have taken out 69 kg of r410a which is the amount stated on data badge.
    acc inlet temperature on slave is -5.7c
    acc inlet temperature on master is 19.7c
    heat exchanger temp on slave is 15.6c
    heat exchanger temp on master is -2.9
    seems opposite to each other
    mitsubishi says low on refrigerant not sure myself now, could problem be reversing valve?

  4. #4
    Join Date
    Feb 2012
    Location
    england
    Posts
    14
    Rep Power
    0

    Re: mitsubishi pury

    acc inlet temp on slave -5.7 on master 19.7
    heat exchanger temp on slave 15.6 on master -2.9
    mitsubishi says low on refrigerant because h/p 13.6 and l/p 2.3 on both units
    could problem be reversing vallve on slave unit?
    any suggestions gratefully received