    Headmaster valve



    I am having problems with a Scotsman Model CME1056. What is the best way to trouble shoot the H.M. Valve. Not looked at it much yet,I am scheduled to do so tomorrow. The system is less than 3 years old (+/- 1 year) always have the tolerance factor. As far as I can tell by just playing with it what little bit I did today the system seems to be charged right ( FLA on the compressor is right on the money ) didn't have a chance to put gauges on it will do so tomorrow. Some where, at some point in time, someone at McDonalds thought that it would be a good idea to tie the condensor of the ice maker in the same cond unit as the walk in freezer and walk in cooler (called a mac ? mack ? system) although I dont like this design, this one is done the same way. anyways I will have some more info tomorrow, if anyone wants to help with the original question now that I have put all of this other useless info down I would appreciate it. (Just venting please excuse)

    Thanks guys
    Justin



  2. #2
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Headmaster valve


  3. #3
    Join Date
    Apr 2006
    Location
    Georgia
    Age
    45
    Posts
    6
    Rep Power
    0

    Thumbs up Re: Headmaster valve

    Took a look at this today and come to find out it was a low charge

    However 2 hours after I returned home to the wife and kids after a 10 hour work day + travel I got called out to the other side of the state for a walk in freezer. The compressor is bad in this one

    A hard working man's job is never done

    Well off to bed for 4 hours and back at again tomorrow.

    Regards,

    Justin

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Headmaster valve

    Sorry I ahve to ask but what's a headmaster valve?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Apr 2006
    Location
    Georgia
    Age
    45
    Posts
    6
    Rep Power
    0

    Re: Headmaster valve

    A valve that is to maintain head pressure during cold weather months. located at the condenser on the high side of the system, (tricks the unit into thinking that the head pressure is higher than it actually is depending on the ambient temp)

  6. #6
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23

    Re: Headmaster valve

    Actually, the Flooded Condenser Control valve (headmaster is a tradename), serves to short-circuit compressor discharge gas around (by-pass) teh condenser coil. This serves to slow the refrigerant flow in the condenser coil.

    The decreased velocity of the refrigerant in the condenser causes the coil to start filling with liquid refrigerant - decreasing the effective area of the condenser and thus maintaining the temperature/pressure of the "high side".

    The process doesn't "fool" anything. It actually does maintain (higher) adequate high pressure by making the condenser less effective during low ambient conditions.

    Advertantly, the discharge gas by-passing the condenser also serves to warm the receiver.


    Cheers!
    Last edited by herefishy; 08-05-2006 at 02:42 PM.

  7. #7
    Join Date
    Apr 2006
    Location
    Georgia
    Age
    45
    Posts
    6
    Rep Power
    0

    Re: Headmaster valve

    Much better said. If I knew everything about them I would not have been on the troubleshooting forum asking how to test them

    The info I provided was given to me by a ref tech as a short explination, I haven't had that much dealing with them as my experience is limited with ice mach.

    Thanks for the explination

    Justin

  8. #8
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Headmaster valve

    Good to see you posting again herefishy.

  9. #9
    Join Date
    Mar 2007
    Location
    USA
    Age
    48
    Posts
    5
    Rep Power
    0

    Arrow Re: Headmaster valve

    hello every body this my first day in the forum.

    well about the head master The way that I check if the headmaster is working properly is feeligng or taking the tempeture on the three tubes of the head master if I feel that the three tubes are on the same temp then is bypassing is the weather is hot the head master is faulty. because is not supposed to be bybassing to raise the presure.

  10. #10
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Headmaster valve

    Good to see Herefishy again. Hello to Justin and Sanchezbond007.

    Herefishy's explanation of a headmaster is one of many that is perfectly correct. I have my own explanation that helps me to understand it. The headmaster is a form of winter condensing pressure control. It is a single valve system that behaves as two valves. A flooding valve, and a receiver pressure regulating valve.

    The flooding valve closes off liquid return from the condenser, and the receiver pressure regulating valve opens a pathway to increase pressure on the receiver.

    So the result is we increase discharge pressure by filling the lower tubes with liquid refrigerant, and we communicate that pressure to the receiver to insure sufficient pressure drop across the TEV and liquid quality to the TEV's.
    The way that I check if the headmaster is working properly is feeligng or taking the tempeture on the three tubes of the head master if I feel that the three tubes are on the same temp then is bypassing is the weather is hot the head master is faulty. because is not supposed to be bybassing to raise the presure.
    The head master has a refrigerant charged dome on it that reacts to the ambient temperature. If the temperature drops, the pressure in the dome drops and permits more refrigerant flow into the receiver and less into the condenser.

    If you lost the charge in the dome, it will tend to bypass the condenser entirely and cause high discharge pressures.

    If you ffeel that the line going into the receiver is as hot as the line going to the condenser when it is warm outside, you can suspect the head master is not working properly. I have known mechanics to take a good knock at the powerhead with a ball peen hammer to get things working correctly again. I am sure that is a loss of powerhead charge temporary solution. I have also seen Schrader valves replacing the charging tube on the dome.. I swear, I did not do it and I promise that I will never do it again.

    I think you understand how it works, from what you said. I just had to rethink all of this for my own benefit.

  11. #11
    CBreeze_2004's Avatar
    CBreeze_2004 Guest

    Re: Headmaster valve

    This is interesting. I've never heard of these valves referred to by any name other than "the headmaster" (often followed by a string of expletives!) -- I was not aware this began life as a trade name!

    What is the general opinion regarding fan cycle control vs. headmasters for maintaining head pressure on txv systems (outdoor condensing units/cold weather ops)? I'm occasionally asked by clients to relocate condensing systems from hot kitchen environments to the roof and always pick the fan cycle option because it's easy. Does anyone think the headmaster is a superior enough pressure control method to warrant the extra time and effort?

  12. #12
    Join Date
    Sep 2007
    Location
    United States
    Posts
    167
    Rep Power
    17

    Re: Headmaster valve

    I've recently learned that condenser manufacturers who use a headmaster valve sometimes do it as a design point. They feel the constant supply of condenser fan airflow is required to control compressor body cooling. They do not suggest changing an original design to a fan control except in a temporary " get out of trouble " situation. I have found more valves with clipped tubes, releasing the charge and opening the valve 100%, this year than ever before. I think it is from techs not knowing how to verify if it works or not. They just cut and run. I install quite a few outdoor units and when ordering the condenser, order a headmaster valve along with a PRV safety from the factory. Here in Chicago, they are code and not worth the violation.
    Don't leave it like you found it.....Leave it like it should be !!!

  13. #13
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Headmaster valve

    Hi Fiesty the originator of this post made this many years ago and has never been back
    My wife used to say you never listen to a word I say at least I think that what she said

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. Scotsman commercial H2O inlet valve
    By fullcourt in forum Trouble Shooting
    Replies: 9
    Last Post: 25-04-2006, 11:41 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •