    Could incorrect settings on solar controller cause constant pressure loss



    Good afternoon,

    I have solar panels installed on the roof, and noticed that the collector temp has been set to 124 degrees! The max recommended setting is 75 degrees. The minimum return temp has been set to -9. Could this be anything to do with why I have no pressure on the solar gauge. It has been topped up numerous times, but the engineers can find no leaks?

    Could having this set so high have any other unwanted effects, or have an impact on efficiency.


    Any comments would be appreciated!



  2. #2
    Join Date
    Oct 2009
    Location
    Norway
    Posts
    39
    Rep Power
    0

    Re: Could incorrect settings on solar controller cause constant pressure loss

    Is the expansion tank working correctly?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Could incorrect settings on solar controller cause constant pressure loss

    If you keep topping up then it has a leak but also check the pressure relief catch tank to see if it has been overpressured.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Dec 2013
    Location
    england
    Posts
    21
    Rep Power
    0

    Re: Could incorrect settings on solar controller cause constant pressure loss

    Hi Brian and Ken,

    I did do some research before I posted and came to the same conclusions as you both ie its either a leak, or the expansion vessel.

    The engineers cannot find a leak. So how would I check if the expansion vessel is working correctly? (it is a 12 litre vessel, pre charged to 2.5 bar) and connected to a daikin altherma LT system

    Thanks

    Is this the same as the 'pressure relief catch tank'?

  5. #5
    Join Date
    Oct 2009
    Location
    Norway
    Posts
    39
    Rep Power
    0

    Re: Could incorrect settings on solar controller cause constant pressure loss

    2.5 bar sounds like precharged from factory.
    I'm not 100% sure how to calculate the pressure.
    I Cant find the formula at the moment. I think it is something with lifting height + 0.1 bar.

    Example expansion vessel is installed before the pump in the basement, and there is 6m to the top of pipes. 1 bar = 10m so 6m = 0.6 bar + 0.1.
    So the air pressure charge should be 0.7 bars.

    Can someone please correct me if im wrong?


    Does the pressure dissapear when the system temperature drops?
    Where is the expansion vessel mounted?
    What's the pressure before and after the pump?
    Have you tried to start the system with cold water and see if the pressure raises with the temperature?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Could incorrect settings on solar controller cause constant pressure loss

    Constant pressure loss is due to evaporation of water at high temperatures through automatic air vents. You should install (if not already installed) special air vents for solar systems with ball valve before air vent. That valve should be closed in normal operation and open only when you venting air for some reason (like change of solar fluid and topping up after fixing leaks).

    http://www.caleffi.com/usa/en-us/cat...r-vent-250041a
    http://www.caleffi.com/usa/en-us/cat...r-vent-na29284
    Last edited by nike123; 22-03-2016 at 09:15 PM.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Could incorrect settings on solar controller cause constant pressure loss

    Quote Originally Posted by Kenneth199 View Post

    Can someone please correct me if im wrong?

    http://www.reflex-pro.de/solaranlage.aspx

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •