Results 1 to 6 of 6

Thread: Sizing question

Hybrid View

  1. #1
    Join Date
    May 2013
    Location
    Australia
    Age
    35
    Posts
    12
    Rep Power
    0

    Sizing question

    Very basic question here as I never do these kind of things but if someone gave you the option of either 1 12kw split or 2 x 6kw splits in a single room what would you choose? Both Toshiba inverters

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Sizing question

    Choosing the size of a split system isn't always about making sure that it can handle the cooling load. You have to also consider the air distribution.

    So if you had a fairly square room with a 12 kW cooling load then a cassette in the middle of the room may do it, but if you had a long thin room with a 12kW cooling load, then 2x 6kW cassettes may be the better option

  3. #3
    Join Date
    May 2013
    Location
    Australia
    Age
    35
    Posts
    12
    Rep Power
    0

    Re: Sizing question

    Yeah makes sense I suppose it always depends on electricity usage a lot of the time too. Cheers mate

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Sizing question

    is this 2x 6kw indoors on a 12 kw outdoor or 2x 6kw systems- typically a cassette will have 4mtr airthrow so as frank says shape of the room is important- if its 9mtr x9mtr then 1 12kw cassette, if its 9mtr x 18 mtr then 2x6kw cassettes- maybe blocking the 2 sides that face each other- in this case 2 seperate outdoors may be better then if a wombat or gecko damages 1 outdoor you still have some cooling

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Sizing question

    Quote Originally Posted by install monkey View Post
    is this 2x 6kw indoors on a 12 kw outdoor or 2x 6kw systems- typically a cassette will have 4mtr airthrow so as frank says shape of the room is important- if its 9mtr x9mtr then 1 12kw cassette, if its 9mtr x 18 mtr then 2x6kw cassettes- maybe blocking the 2 sides that face each other- in this case 2 seperate outdoors may be better then if a wombat or gecko damages 1 outdoor you still have some cooling
    Unlike Manchester where it would be feral cats and drug users

    Did I ever tell the story of the drug user stealing R410A because he was told
    it would give him a buzz.................



    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Sizing question

    I would use two independent splits. If conditions are too hot for one, fire up the second. If possible, have the outdoor units wall mounted and separated. Way too many critters ( crawling, jumping or flying ) are attracted to ground mounted units.
    Have a sparky hard wire them to independent Circuit breakers at your Meter box.