    Mar 2016
    Sri Lanka
    33
    1
    Replaced the compressor. Not cooling properly.
    Hi everyone,
    I've replaced a compressor (R22) of a 36000BTU cassette type air conditioner. The unit is not cooling properly. The pressure of the high side is around 220 and the low side is around 70. The outdoor coil is not heating as it should be. The ambient temperature is around 95 (35) degrees and the minimum temperature of the cold air that blowing out from the indoor unit is around 77 (25) degrees. What could be the problem?
    Thanks.
    4,697
    Re: Replaced the compressor. Not cooling properly.
    Hi Vikum24.
    Welcome to the forum.
    Could you tell me what subcooling you are getting?
    3,856
    Also was it the correct compressor? Correct amount of R22 added? What made the original compressor fail?
    Sep 2003
    ISRAEL
    72
    4,248
    4 way valve?
    Jul 2010
    NTH.QLD Australia
    1,730
    32
    Low pressure exceeding 70 PSI is common when starting an R22 split in 35 Deg C Ambient. You have to find the compressor Current draw with an Ammeter and compare your reading to compressor running Amps found on the Compressor sticker.
    + 10 Degrees C temperature differential at the Evaporator is common if your Air-conditioner is Short of Refrigerant.
    Feb 2007
    2,473
    Did you ensure you had a deep vacuum in the system before you recharged it with refrigerant?