Thread: Daikin Controllers
-
02-05-2006, 02:13 PM #1
Daikin Controllers
I am doing a quote for Daikin 2 Multi splits (2MXS40D and 3MXS40D) With 5 indoors, 3 x FTXS20DW, 1 x FTXS25DW, 1 x FTXS35DW.
I know with Daikin VRV you have to buy the controllors seperate. Is it the same for the splits and multi-splits?
The reason I ask is because I remember a few years ago someone at the company I used to work for in England quoted for 150 splits (cassettes) and forgot that the facias were seperate.
This will be the first time we use Daikin Espaņa and in the catalogue there is no mention of controllers in the splits and multi-splits section.
Anyone any idea?
regards
paul..
-
02-05-2006, 03:50 PM #2
Re: Daikin Controllers
Hi Paul
The 2MXS40D has 3.9kw total cooling capacity (UK Conditions) = 27C outdoor 21C indoor. If you are connecting 1x FTXS20's and 1 x FTXS35 then, in your ambient conditions you will only get slightly less than these duties.
You can't get a 3MXS40 - it's a 3MXS52 and fitting 3 x FTXS20's will give about 1.78kw per room.
The wall mounted fan coil units come with their own infra red remote controller so don't worry. It's only on the hard wired controllers where sometimes you have to buy them seperately.
I've attached spec sheets for the units
-
02-05-2006, 04:03 PM #3
Re: Daikin Controllers
Thanks Frank.
The outdoor unit is a 3MXS52D I typed it wrong.
The 3 x 20īs are going in bedrooms and the load is only around 1.6-1.9kW and according to the my catalouge the nominal cooling should be 1.73kW. Itīs unlikely that all 3 units would be run at the same time, so they should be fine.
Is that information you posted from the UK catalouge? My spanish version has different values in the capacity tables for the same models? Maybe they are tested at different temperatures or something?
Cheers,
PaulLast edited by airefresco; 02-05-2006 at 04:07 PM.
-
03-05-2006, 07:59 AM #4
Re: Daikin Controllers
Originally Posted by airefrescoThe 2MXS40D has 3.9kw total cooling capacity (UK Conditions) = 27C outdoor 21C indoor. If you are connecting 1x FTXS20's and 1 x FTXS35 then, in your ambient conditions you will only get slightly less than these duties.
Look at the bottom of the attachments - it states the operating conditions
As you know - we don't get as much sun as Spain
-
03-05-2006, 09:04 PM #5
Re: Daikin Controllers
Hi there as for the controllers like frank said split and multi spilt all come with infra red controllers. The hard wired controllers are not an option for these units. Its only when you move up to the sky air range. But i hear soon there will only be one range of fan coils for split/multi split and sky air
-
15-05-2008, 08:08 AM #6
Re: Daikin Controllers
Gents, Check out the Daikin web site, You can now fit a standard wired controller to the split range witha small adaptor pcb(remember to order the little connection cable).
We fit these if the unit is in a small server room,(stops the IT techy guys running off with them!)
Similar Threads
-
Daikin Euwa
By RysioZklanu in forum CommercialReplies: 9Last Post: 20-07-2011, 02:51 PM -
Daikin Refnet Position
By puddleboy3 in forum Air ConditioningReplies: 15Last Post: 13-02-2009, 04:12 PM -
New to RE and needing Daikin Help
By Owen in forum Air ConditioningReplies: 20Last Post: 25-09-2008, 06:55 PM -
Daikin Analyzer
By marc5180 in forum FundamentalsReplies: 10Last Post: 02-08-2008, 07:15 PM -
!!big Daikin Problem!! Codes,u4,pj, And E0
By airconengineer in forum Air ConditioningReplies: 21Last Post: 31-05-2007, 09:04 PM