    BTU/KW Sizing advise please



    My friend bought a new house last year. He is doing the house up and redecorating it and wants air con installing (wall mounted units) here are the sizes etc.

    The house is well insulated with Cavity Wall and lots of loft insulation. I said I would find out what he would need before he calls a company out so he has an idea of what he is looking at. I've used lots of calculators with differing results - ive put down below what the results are that I have got from websites.


    Room sizes are as follows in meters.
    Lounge
    4.26(l) x 4.26(w) x 2.64(h)
    Usual TV and sofa arrangement with seating for 4 people – 6 at a push. Usually only 2-3 people sat in here. This room is separated by the kitchen by a door. Off of the lounge is a small hallway with stairs to the landing. The window in this room faces South East. Gets the sun first thing in the morning which is gone by midday. Was thinking a 7000 btu unit?


    Kitchen,
    5.18(l) x 3.35(w) x 2.74(h)
    Has a dining table that can seat 4 people and a breakfast bar that seats 2 people, usually 2 people through the week though. Gas hob with 5 rings along with a fan oven. Cooking is usually on weekends where we have all the hob fired up and oven. The kitchen is an entrance to the house from the garden and if having BBQ's or entertaining the kitchen external PVC door is left open. Kitchen window and door faces North West. Gets the sun from about 2pm until sunset if were lucky to have summer. - maybe a 3.5kw unit)


    Main bedroom
    4.26(l) x 4.26(w) x 2.64(h)
    Faces South East, sun shines in on a morning. - possibly a 7000btu unit?


    Second bedroom, Currently has a 7000btu unit (2.1kw)
    3.35(l) x 3.35(w) x 2.64(h)
    Smallest room in the house, this faces North West. - possibly a 5000btu unit?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: BTU/KW Sizing advise please

    CIBSE 'Rule of Thumb' calcs are based on square metre floor space x 125w

    i.e. for the Lounge, 4.26 x 4.26 x 125 = kW heat gain

  3. #3
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: BTU/KW Sizing advise please

    Quote Originally Posted by frank View Post
    CIBSE 'Rule of Thumb' calcs are based on square metre floor space x 125w

    i.e. for the Lounge, 4.26 x 4.26 x 125 = kW heat gain
    But what about ceiling height etc?

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: BTU/KW Sizing advise please

    Unless the ceiling is over 3m I wouldn't factor it in. In a house trying to factor in solar gain (unless it's a conservatory) is going to lead to over sized units, plan for the 80/90% of conditions it will actually see, unless they have unlimited budget? I would if possible suggest upping the insulation, both wall and attic, money spent here pays bigger dividends, should also reduce required capacity on air con.

    As frank suggests, CIBSE's rule of thumb is as good as any sizing program I've seen.
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: BTU/KW Sizing advise please

    Quote Originally Posted by al View Post
    Unless the ceiling is over 3m I wouldn't factor it in. In a house trying to factor in solar gain (unless it's a conservatory) is going to lead to over sized units, plan for the 80/90% of conditions it will actually see, unless they have unlimited budget? I would if possible suggest upping the insulation, both wall and attic, money spent here pays bigger dividends, should also reduce required capacity on air con.

    As frank suggests, CIBSE's rule of thumb is as good as any sizing program I've seen.
    Ok seems reasonable.

    So got the lounge and bedrooms sorted what would you put in the kitchen? A 3.5kw to cope with the heat from the oven and the hob when cooking?

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: BTU/KW Sizing advise please

    I'd be careful in the kitchen due to the potential for grease laden air and a 'domestic' split.

    Very, very regular cleaning may be required.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: BTU/KW Sizing advise please

    For sure they will be kept clean, his kitchen extract also vents to the outside.

    What would you advise for the KW for each room and I can check to see if this fits with my calculations?

    Many thanks for your advise so far.

    I was thinking a 9000btu for the kitchen to allow for cooking, (7000btu without the cooking) a 7000btu for the lounge, 7000 for the main bed and a 5000btu for the small bedroom. Or do I go for a 1200btu for the kitchen, cant work out the heat gain for kitchen as seen somewhere else that you add on 4000btu for kitchens but is this commercial?

  8. #8
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: BTU/KW Sizing advise please

    Turn off the split in the kitchen when cooking, otherwise you'll be taking the indoor off the wall to degrease every few months, again this is not commercial so KISS. a 2.5 would do the kitchen.
    Mostly found in the southern part of this green and pleasant land.

  9. #9
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: BTU/KW Sizing advise please

    Thank you for your input.

    When cooking though he does no frying all is done in the oven or boiling things on the hob and he has the extractor running when he does to help clear the steam. There is no frying at all.

    If you are using it when cooking what would you put in then?

    Oh and what would you reccomend for the lounge and bedrooms?
    Last edited by back2space; 08-03-2016 at 08:27 PM.

  10. #10
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: BTU/KW Sizing advise please

    Guessing North East would be somewhere in England. Kitchens have a tendency to grease the filters and eventually clog the Evaporator... extraction fan or not. Comments above are spot on.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  11. #11
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: BTU/KW Sizing advise please

    Yes this is in England. There is no grease in his kitchen, he does not fry etc only oven bake. The hob is only used to boil.

  12. #12
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: BTU/KW Sizing advise please

    Hob?... Sheet, I'll have to ask Wicki for a translation.
    Last edited by mikeref; 10-03-2016 at 10:22 AM.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  13. #13
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: BTU/KW Sizing advise please

    Quote Originally Posted by mikeref View Post
    Hob?... Sheet, I'll have to ask Wicki for a translation.
    Hob being the top part with the gas rings on lol.

  14. #14
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: BTU/KW Sizing advise please

    Hi, mikeref
    Quote Originally Posted by mikeref View Post
    Hob?... Sheet, I'll have to ask Wicki for a translation.
    if you have a problem with meaning of English words .... don't even try to imagine my problems sometime ...there is no Wiki or similar dictionary to help me to find a real meaning and to ask for explanation is not always "easy" ....

    fortunately, this above (hob) is explained well with images ...

    ... for that reason it is nice to use as much as possible simple and known words , not only for me ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  15. #15
    Join Date
    May 2008
    Location
    England
    Posts
    37
    Rep Power
    0

    Re: BTU/KW Sizing advise please

    I would skip the kitchen, unless it is also a dining room.

    If also a Dining room then locate the air-conditioner away from the cooking area (opposite wall?)
    Last edited by Good^Man; 06-08-2016 at 02:31 PM.

  16. #16
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: BTU/KW Sizing advise please

    Quote Originally Posted by Good^Man View Post
    I would skip the kitchen, unless it is also a dining room.
    yes a kitchen diner.