Thread: Flower cooler
03-03-2016, 08:16 PM #1
Flower cooler
Hello,
I am new to the forum. My wife has a floral business and is asking me to turn a room in our warehouse to a cooler. The room is about 10'x20'x10'. I am looking to do it the simplest and cheapest way possible. I have seen some coolers like this in the flower market where we buy the flowers from. Any ideas would be greatly appreciated.
03-03-2016, 08:45 PM #2
Re: Flower cooler
i suggest you consult your local hvac engineer
03-03-2016, 10:23 PM #3
Re: Flower cooler
Flowers are funny things, there still alive and give off fumes, moisture and heat
and therefore you don't want a normal cooler. The nearest thing that is a
easy install is a produce fridge (you know, Brussels sprouts, brockley and others).
It does need to be correctly done otherwise you will either dry the flowers out or
mold and fugus will grow.
Rob
04-03-2016, 12:34 AM #4
Re: Flower cooler
my book states general storage condition for flowers at 90 to 95% RH and average 2.5 ' C dry buld
04-03-2016, 03:45 PM #5
04-03-2016, 06:12 PM #6
Re: Flower cooler
Have kept up humidity in produce room where evap drains into top tiers of 4inch plastic guttering with capped ends fitted with raised overflow tube draining down to next tier and final level raised overflow drains to outside. Everything kept well and hi humidity. A good level of water with a good surface area. The guttering was the full width of the room on the wall below and behind the evap.saw it in use once then did it for more fruit and veg customers. Simples.
05-03-2016, 02:55 AM #7
Re: Flower cooler
keep all condensate with in the room to maintain max humidity.
06-03-2016, 05:59 PM #8
Re: Flower cooler
I have done tow big flowers cold rooms in the past for a local florist.
The temp he wanted was 8C with 85% to 90% humidity. Used two large dual discharge evaporators with large fin spacing to avoid drying the air. Two ultrasonic humidifiers for extra humidity when needed.
The use of dual discharge evaporators was to avoid direct air flow on the flowers so they will not dry.
The time you store the flowers is critical, for a short time up to 48 hours in a small room you can simply add humidity with a hand held spray and get low speed fans to keep the air wet.
The cooling unit should be about 15% larger to cool the humid air.
07-03-2016, 08:55 AM #9
Re: Flower cooler
In my region, Flowers are divided into Categories. Some rooms run at +2 degrees C while exotic varieties can't withstand anything cooler, so +6 to +8 degrees C is needed.
All varieties are placed in buckets of fresh water, and there has to be no wind chill from the Evaporator.
Evap condensate is drained outside.
Absolutely NO Ripening fruit or Vegetables allowed in any flower Coldrooms.
