    Ammonia Wet Return Line
    Hello,
    Please let me know what is the selection criteria of wet return line of ammonia?
    and what will be the suitable line size for ammonia wet return line if the cooling capacity is 287 kW and circulation ratio is 4?
    Auckland
    68
    3,362
    32
    Re: Ammonia Wet Return Line
    Large is the short answer.
    sorry a little politeness goes a long way, and a lot more information required.
    Jan 2006
    Croatia
    2,136
    Hi, Ubaid Rehman welcome to RE forums .... please, it is not needed to ask almost the same question twice ... put all you need in one question .... it is easier for you and for us ....
    Quote Originally Posted by Ubaid Ur Rehman View Post
    Hello,Please let me know what is the selection criteria of wet return line of ammonia? and what will be the suitable line size for ammonia wet return line if the cooling capacity is 287 kW and circulation ratio is 4?
    Hi,I'm using danfoss coolselector 2 software for selection of liquid and wet return line of ammonia refrigeration system. It provides 3 selection criteria for that which are as below:
    1. Pressure Drop or Velocity
    2. Pipe Size
    3. Saturated Temp. Drop (0.02K/m)
    Please guide me which one is most accurate one and what is the default value of pressure drop in this software? and what are the recommended velocities for both lines?
    to get a good suggestion you must give us as much as possible data regarding your question ... i.e. evaporation pressure/temp, condensing pressure/temp, distance from evaporator to suction separator ...
    Best regards, Josip