    Refrigerant r32 pipe connections



    Hi all,

    I have been asked if I can install a Daikin FTXZ25N / RXZ25N wall mounted split system that operates on R32.

    We didn't supply it. The householders' father purchased it in France and gave it to his son as a gift. Looking at the installation manual it states that the indoor unit flare connections must be made off outside of the building, but on another page it details how to install the pipes and connections inside.

    Confusing to say the least. Does anyone know what the requirement is? We haven't yet taken the plunge into R32, we are waiting to see if the gas is as bad as R407C

    Cheers fellas


    My tools. Screw driver, Hammer & a Condom:
    If you can't fix it, hit it. If you can't hit it, F**k it!

  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Refrigerant r32 pipe connections

    Danfoss have written some interesting stuff about it.
    http://refrigerants.danfoss.com/r32/

  3. #3
    Join Date
    Nov 2005
    Location
    wales
    Posts
    66
    Rep Power
    20

    Re: Refrigerant r32 pipe connections

    Daikin's paper on R32
    http://www.daikin.co.uk/binaries/334...511-342471.pdf
    On wall mounted units I generally cut the flares off and braze the copper straight on so less likelihood of problem with leaks behind the unit or in buried the wall in the future.
    You should also work out the refrigerant charge to room volume ratio, so even if you get a leak, then it will be below the flammability %.

  4. #4
    Join Date
    Nov 2006
    Location
    Guernsey
    Age
    65
    Posts
    237
    Rep Power
    18

    Re: Refrigerant r32 pipe connections

    Yes, thank you for that. I was thinking about cutting the flares of and brazing, but not yet having had my hands on a system i was sure if there was a strainer close to the flare. I guess the connections are identical to R41A units then.

    I will have to speak to the guy that has purchased the unit to see what the room dimensions are. I have read the install manual, hence my question as it is a tad confusing as it says 2 different things about the connections.
    My tools. Screw driver, Hammer & a Condom:
    If you can't fix it, hit it. If you can't hit it, F**k it!

  5. #5
    Join Date
    Feb 2016
    Location
    UK
    Posts
    5
    Rep Power
    0

    Re: Refrigerant r32 pipe connections

    Hi Guys

    It is illegal to install R32 splits in UK with flare connections inside the building. R32 is classed as an A2L refrigerant which has a risk of combustion.( Very light risk and highly unlikely that combustion would occur) R32 needs a limit density of 13 % + vs air and an ignition source exceeding 640 degrees C. But anything can happen.

    Cut the flares off the indoor unit, or as you said install the flares outside if possible
    I cannot speak for Daikin but with our R32 units we recommend removing the flares on the indoor side if the connection is to be made indoors.

  6. #6
    Join Date
    Mar 2014
    Location
    Australia
    Posts
    36
    Rep Power
    0

    Re: Refrigerant r32 pipe connections

    Best to cut and weld. I have had a few which are ok until you move the pipework a little, then they leak.

  7. #7
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Refrigerant r32 pipe connections

    Attended the Daikin R32 course and nothing was mentioned about flare nuts inside unless this has changed recently. However a min floor area is required depending on unit size and charge in case of leakage.

  8. #8
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Refrigerant r32 pipe connections

    Proper mental.

  9. #9
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Refrigerant r32 pipe connections

    Solder all? No brained,but who would do jobs for family? you only get paid in love and that lasts for how long in families?

  10. #10
    Join Date
    Aug 2010
    Location
    England
    Age
    53
    Posts
    77
    Rep Power
    16

    Re: Refrigerant r32 pipe connections

    Quote Originally Posted by Panasonic-Tech View Post
    Hi Guys

    It is illegal to install R32 splits in UK with flare connections inside the building. R32 is classed as an A2L refrigerant which has a risk of combustion.( Very light risk and highly unlikely that combustion would occur) R32 needs a limit density of 13 % + vs air and an ignition source exceeding 640 degrees C. But anything can happen.

    Cut the flares off the indoor unit, or as you said install the flares outside if possible
    I cannot speak for Daikin but with our R32 units we recommend removing the flares on the indoor side if the connection is to be made indoors.
    The chap is on Guernsey. Although part of the Uk they are not part of the EU....or something like that??! I've done quite a bit of work there at Cable & Wireless and they do things a little differently on the rock

  11. #11
    Join Date
    Nov 2006
    Location
    Guernsey
    Age
    65
    Posts
    237
    Rep Power
    18

    Re: Refrigerant r32 pipe connections

    Yes, thanks for the responses, that was my point the install manual states that the flares should be made off outside the building then on another page shows how to make them off and insulated them as per normal behind the wall mount unit. Very silly Daikin!! I would myself cut and shut them as little chance of a leak that way. And Gideon, you are correct, many of the things they do here are different to the UK. What is it you did for Cable & Worthless? Data centre cooling perhaps?
    My tools. Screw driver, Hammer & a Condom:
    If you can't fix it, hit it. If you can't hit it, F**k it!