    Talking Daikin FLXS50/RXS50



    Hi Guys,
    Have a prob with a U4 fault on this single unit, have 30vdc coming of outdoor unit comms to earth wire 2vdc of indoor unit.
    Checked drain -all clear, powered down and up no joy.
    Flaps opens and closes on indoor -power 230v ok
    suspect indoor unit pcb, any advice would be welcome



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin FLXS50/RXS50

    I would run a temporary single core wire between terminal 3 of the indoor and outdoor units to see if that solved the problem

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin FLXS50/RXS50

    Check that terminal 1 and 2 on indoor and outdoor are correctly wired ( not mixed)!

  4. #4
    Join Date
    Feb 2016
    Location
    West Sussex England
    Age
    34
    Posts
    9
    Rep Power
    0

    Re: Daikin FLXS50/RXS50

    I may be your saviour.

    Is the led lit on the outdoor pcb?

    if not, unplug outdoor fan motor, is it now lit (blinking)

    try the outdoor eev head too,

    had this fault on many daikin units,