Thread: Daikin FLXS50/RXS50
-
02-03-2016, 02:45 PM #1
Daikin FLXS50/RXS50
Hi Guys,
Have a prob with a U4 fault on this single unit, have 30vdc coming of outdoor unit comms to earth wire 2vdc of indoor unit.
Checked drain -all clear, powered down and up no joy.
Flaps opens and closes on indoor -power 230v ok
suspect indoor unit pcb, any advice would be welcome
-
02-03-2016, 07:51 PM #2
Re: Daikin FLXS50/RXS50
I would run a temporary single core wire between terminal 3 of the indoor and outdoor units to see if that solved the problem
-
02-03-2016, 08:03 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Daikin FLXS50/RXS50
Check that terminal 1 and 2 on indoor and outdoor are correctly wired ( not mixed)!
-
13-03-2016, 05:47 PM #4
Re: Daikin FLXS50/RXS50
I may be your saviour.
Is the led lit on the outdoor pcb?
if not, unplug outdoor fan motor, is it now lit (blinking)
try the outdoor eev head too,
had this fault on many daikin units,