    Exclamation Vacuum condition problem



    Hello all i just bought vacuum gauge Testo 552 and connect it to vacuum pump and Testo 550.

    So when i start to pull the vacuum is ok, after that I close the valve on the Testo 550 to isolate the pump and I turn off the pump.

    So all the measurements which i can see are from the vacuum between the Testo 550, ribber hoses and Testo 551

    As you can see from the video which i took the vacuum is not stable and when i close the valve from the T550 vacuum level going more weak (rise up).

    Here is the video
    https://www.youtube.com/watch?v=bkkVvEiyw5o

    PLease let me know why is that happen?



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Vacuum condition problem

    Chriss,
    This may help as see that permeation occurs in hoses & fitting leak if not "0" ring type.

    http://alltemp.ca/wp-content/uploads...Presention.pdf

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Vacuum condition problem

    Still not able to give you rep points Ranger.
    An Interesting read all the same.
    Thanks Grizzly
    Despite the High Cost of Living it still remains Popular!

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Vacuum condition problem

    I have seen similar vacuum rise, i think i read somewhere that is is because the volume of what you are measuring is so small (just the insides of the hoses) it should not behave the same way on a system. Also if they are new hoses they will give of fumes (new rubber smell) which will affect the vacuum reading until they have aged a bit.
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Vacuum condition problem

    I Quote from Rangers Link!
    Read the last paragraph in particular.

      Always a good idea to attach a micron gauge to the vacuum pump to make sure the pump
    pulls down to at least 50 microns.?
      If it doesn’t, your pump oil is contaminated and should be changed.?

    Do not shut off the blank-off valve on the pump and expect the gauge to hold a
    vacuum as the gauge will fall back to atmosphere.

    (The sensor in the gauge is too close to the pump and does not have time to
    equalize).

    Grizzly
    Despite the High Cost of Living it still remains Popular!

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Vacuum condition problem

    When i vacuum a big unit, I use these two gauges to make sure it stays or leak.

    images.jpgהורד.jpg

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Vacuum condition problem

    This is also interesting link, thanks for rep points ms.

    https://www.youtube.com/watch?v=cI6pSBaskjc
    Last edited by RANGER1; 28-02-2016 at 09:30 PM.

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Vacuum condition problem

    Do you ever sleep
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Vacuum condition problem

    Quote Originally Posted by Grizzly View Post
    Do you ever sleep
    Grizzly
    Grizzly the second link is the one I was looking for in the first place, as thought it was pretty good.
    I look at things on IPhone a lot so can look anywhere at anytime.
    Had about 9 hrs last night��
    Last edited by RANGER1; 29-02-2016 at 07:17 AM.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Vacuum condition problem

    The only connecting lines that are absolutely vacuum tight are soft copper tubing or flexible metal hose