    Can anyone lead me in the right direction on diagnosing this tk unit thanks



    Hello fellow techs i have a 2007 thermo king sb200 and i would like to know how do
    i preform a three way valve test .this unit needs refrigerant about every two weeks. There is no visible leaks, i checked for leaks with a leak detector and also put nitrogen in the system and still can not find any leaks. I preform a low side pump to 25 vac and suction side rises above 0 on
    gauges within seconds.
    Can anyone help thanks



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Can anyone lead me in the right direction on diagnosing this tk unit thanks

    Throttling valve,there. Is a vent hole on the back of it test there,also compressor shaft seal maybe another leakage points plus the gaskets on the discharge manifold.

  3. #3
    Join Date
    Feb 2016
    Location
    united states
    Posts
    3
    Rep Power
    0

    Re: Can anyone lead me in the right direction on diagnosing this tk unit thanks

    Hey thanks i will test the throttling valve.later today do i need to have a compound gauge or can i check it with my manifold gauge. Also i replaced the shaft seal already, throttling valve gasket, and the discharge manifold gaskets and it's still been loosing refrigerant

  4. #4
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Can anyone lead me in the right direction on diagnosing this tk unit thanks

    There is a vent hole at back best tested with soap solution with unit not running

  5. #5
    Join Date
    Feb 2016
    Location
    united states
    Posts
    3
    Rep Power
    0

    Re: Can anyone lead me in the right direction on diagnosing this tk unit thanks

    Quote Originally Posted by cadwaladr View Post
    There is a vent hole at back best tested with soap solution with unit not running
    thanks i will try this and let you know the out come