    R111
    I would like to use a SOLAR COLLECTOR as an evaporator for an R111 system that would heat water through a chiller.
    Thoughts?
    Aug 2005
    5,302
    Re: R111
    I did a quick search for this fluid.
    R-111 = pentachlorofluoroethane
    Boiling point = 275F [135C]
    My first thought (& question) is: This has chlorine in it, so is it permissible for use? It is listed as a CFC.
    Second question: This has ethane also, so you need to be aware of the need for intrinsic safety with electrical devices.
    If the collectors generate a sufficient temperature to boil this fluid, why do you need a chiller? The heat sink (the lower temperature you are rejecting heat to) will be low enough to condense the refrigerant at temperatures high enough for space heating.
    You could use a refrigerant pump to circulate the fluid.
    1) boil the refrigerant in the collectors.
    2) the refrigerant vapor travels to the cold heat sink and condenses to a liquid
    3) The refrigerant condensation process heats the water
    4) the refrigerant pump circulates the condensed refrigerant back to the collectors for boiling again.
    The idea is reasonable, but I don't think the fluid is suitable.
    Jun 2005
    S****horpe
    135
    Re: R111
    It is a CFC so won't be flammable - no hydrogen in it (the "ethane" bit only tells you about the backbone of the molecule that the Fs and Cls are attached to). Think you're right, wouldn't a lower boiling point be more suitable? Unless kettler means R11, but then that would be a bit low?
    It's a lovely day to pump some gas
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: R111
    Why not using a water/water heat pump with std solar collector and a more environmental friendly refrigerant?
    That type of HP would help in keeping the charge low...
    Apr 2006
    65
    34
    Re: R111
    Thanks everybody. I appreciate the information and dialoge.
    Apr 2006
    65
    34
    Thumbs up Re: R111
    Thanks! I think the refrigerant I picked is incorrect. Will look into.
    Quote Originally Posted by US Iceman
    Aug 2005
    5,302
    Re: R111
    Quote Originally Posted by Johnny Rod
    ...the "ethane" bit only tells you about the backbone of the molecule that the Fs and Cls are attached to)
    Thanks for that. I am certainly no chemist. Can you provide a short explanation why the ethane becomes non-combustible?
    If we bypass the CFC issue, the fluid could work if the Pressure/Temperature relationship does not exceed the design pressure limits for the collectors and system.
    I think a lot of this depends on the type of collector (flat plate or concentrating and/or tracking capability). If the fluid can evaporate at 275F [135C] at atmospheric pressure it can also condense at the same temperature.
    The lower heat sink temperature would be less than 275F [135C], so this could generate hot water (pressurized) or steam at atmospheric pressure. A simple thermosiphon, except the liquid would have to be pumped to the collector panels, if the heat sink is lower than the panels.
    R-114 has been used in a similar application except I believe the system did use a compressor to circulate the refrigerant around the system.
    Jun 2005
    S****horpe
    135
    Re: R111
    It's part of the IUPAC naming convention. Ethane means the molecule has a backbone of 2 carbon atoms (methane is 1, propane is 3, butane is 4 but can be straight or T-shaped) and has 6 attachment points. When it's preceded by mono-/di-/tri- fluoro-/chloro-/bromo- etc. then these atoms are attached to the backbone. Any leftover spaces are taken up by hydrogen atoms - in ethane istelf there are only hydrogens attached (it is a HC). More hydrogen atoms means more flammable (HCFCs, HFCs). No hydrogens (CFCs and FCs) means not flammable, except at high temps. Pictures work better but I don't have anything to hand.
    Apr 2006
    65
    34
    Re: R111
    I'm looking for a list of REFRIGERANTS and their corresponding BOILING POINTS. Does anyone know where I can obtain the information?
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: R111
    Try coolpack or refpack in the database section above
    Jan 2006
    Croatia
    68
    2,261
    31
    Re: R111
    Hello Kettler,
    you can download this to see:
    http://www.airah.org.au/downloads/AIRAH_RSG2003.pdf
    maybe you can find something more at: http://www.airah.org.au/
    Attached file is not complete (need to extract some pages to reduce file size)
    Here at "Andy's HVAC/R Web Page" you can download REFPROP v1.0 Calculator for 38 refrigerants and some other useful things
    http://users.isp.com//aschoen/
    Hope this will help, come back with comments, please
    Best regards,
    Josip
    Attached Files Attached Files
    Apr 2006
    65
    34
    Re: R111
    Thanks! I'm looking at the information you provided and will get back to you.
  1. Replacements for R11 and R111?
    By jlnelson in forum Refrigerants