Results 1 to 12 of 12
    Sep 2012
    Sweden
    49
    12
    Relative humidity in a freeze room
    I have some questions regarding RH in a Freeze room. I have checked that the door and the rest the room is sealed off with extra around the door. When I start the freeze room I have about 35 % RH and 21 degrees. Every eight hour the defroster starts. After a couple of days I turn of the freezer and keeping the door closed and i get 100 % RH. Is the graph below evidence that my freeze room is not sealed off enogh?
    The reason I keep the door closed after I turning the freezer off is a project where they are testing pest infected wood and they want to rise the temperature slowly.
    So any suggestion on how to keep the RH down in my freezer room.
    Lars
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Relative humidity in a freeze room
    I dont know about 100% but it will be around 95%.
    You can do the same outside and see that it is almost the same.
    Sep 2012
    Sweden
    49
    12
    So it is a normal behaviour that it rises to 95% when i have a completely sealed freez room. Should it not go back to 40% when temperature rises?
    Sep 2003
    ISRAEL
    72
    4,248
    No, it will stay like that.
    If the room is not sealed, you will notice a lot of ice on the evaporator and frost on the outside where heat enters the room.
    If you want low humidity, you should consider using in addition to the cooling unit, molecular sieve drier with dew point of -40C.
    That will dry the air very well
    Somerset
    69
    4,697
    Hi Lars.
    Just out of interest what happens if you disable the defrosts?
    Because all that moisture trapped as Ice, then melted so that it flows away as water.
    Will re-introduce some Humidity!
    As Chemi states if your door is leaking you can turn off the threshold heater and watch the ice build up.
    Have you considered changing your defrost cycle and have you looked at your drain pipes and Vapour seal lately?
    Jul 2010
    NTH.QLD Australia
    1,730
    32
    External dehumidifier in a closed circuit with your freezer room. It would have to be undersized to allow your refrigeration kit to reach the temperature required, though it must have the capacity to remove moisture with minimal temperature elevation.
    The defrost cycle can't be avoided so a thermostat and Humidistat have to be wired in series with this dehumidifier.
    Proof reading sorta reminds me of this Gem. Thanks Monkey Spanners and Install Monkey
    https://www.google.com.au/url?sa=t&r...kYPdzTzMOJnR3Q
    Sep 2012
    Sweden
    49
    12
    Thanks for the answers.
    I will try to change the defrost cycle and see what happends. The freeze room have two pressurerelief valves, could they have something to do with it if i have constant under preussare in the freeze room.
    Lars
    Sep 2003
    ISRAEL
    72
    4,248
    Before changing the defrost parameters, you should check if there are any problems with it.
    Pressure relief valves are only there to protect the system from over pressure, do not touch them.
    Sep 2012
    Sweden
    49
    12
    Tested and I have a steady flow of fresh air in to the freezer via the two pressure relief valves. It is a small freeze room, about 15 m3. I cannot find or think of any other way that the fresh air enters the freeze room and gives me the high RH. The door is completely sealed off, no ice buildup what so ever.
    What is the worst that can happend.
    Sep 2003
    ISRAEL
    72
    4,248
    Auckland
    74
    3,357
    37
    hello Lars.
    check out.
    www.kwangu.com/work/psychrometric.htm
    lowering the dry buld temp will ramp up the RH plus air density will change , balance ports manage pressure differences and draw fresh air in, or exhaust air during defrost and density change
    With sub zero temps the RH will be high but absolute humidity will be low.
    Research a desicant drier to maintain low RH continuosly.
    Mar 2016
    Australia
    55
    3
    For strict lab type conditions for constant r/h and temp. control you
    really need a second form of dehumidification and cooling for closer
    parameters. A second coil could be your problem solver.