    Daikin Super Inverter



    I just install a new pc board to this condensing unit and it just wont work error code is UA can someone assist



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Daikin Super Inverter

    https://www.climatecenter.co.uk/wcss...in-trouble.pdf

    Looks like there are some dip switches or similar that need setting for it to work, its wired wrong, or its the wrong board.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin Super Inverter

    why was the board changed?- what was the original fault?
    some daikin pcbs req a capacity setplug that tells the pcb the size of the outdoor unit