york chiller ycas model dxs compressor high motor current its an emergency pls reply
hi friends i have one chiller york YCAS model screw compressor one time starting properly second time when starts star winding after did not changed to delta before alarm coming high motor current
-
18-02-2016, 04:22 PM #2
Re: york chiller ycas model dxs compressor high motor current its an emergency pls r
Check that the star/delta timer is operating correctly.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
18-02-2016, 05:18 PM #3
Re: york chiller ycas model dxs compressor high motor current its an emergency pls r
iam new this chiller that timer on board how i check
-
21-02-2016, 01:22 PM #4
Re: york chiller ycas model dxs compressor high motor current its an emergency pls r
ptc sensor how working
-
21-02-2016, 09:18 PM #5
Re: york chiller ycas model dxs compressor high motor current its an emergency pls r
kill the 3 phase to the contactors to check the star delta operation- maybe a sticking contactor
-
28-02-2016, 02:31 PM #6
Re: york chiller ycas model dxs compressor high motor current its an emergency pls r
u said correct dear board problem