    Pressure switch set up



    Hi, looking for help.

    For setting up a cold room to to run between 3oC-5oC on R134a gas with a 35oC average ambient temperature, what should I set my pressure switch to cut in and out at?
    It's a thermostat controlled pump down system, Thanks.



  2. #2
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Pressure switch set up

    3 psi and 35 to 40 Psi if it is a TX system that hasn't had it's valve fiddled with.
    Might as well grab a PT chart from your local distributor.
    Last edited by mikeref; 17-02-2016 at 08:44 AM. Reason: added some.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Pressure switch set up

    Quote Originally Posted by SteG View Post
    Hi, looking for help.

    For setting up a cold room to to run between 3oC-5oC on R134a gas with a 35oC average ambient temperature, what should I set my pressure switch to cut in and out at?
    It's a thermostat controlled pump down system, Thanks.

    Cut out pressure should be above 0 kpa so system never goes in vacuum

    3 deg C = 226 kpa
    5 deg C = 250 kpa
    suction pressure would probably operate at about -6 deg C or 130 kpa

    suggest cut out pressure between 20 to 50 kpa, depending on size of evaporator.
    You don't want really long pump down time & it could pump down a few times during off cycle.

    suggest cut in pressure 226 kpa or 3 deg C = lower limit of room temp.
    If it takes to long to start lower it a bit, as you want to avoid any floodback on start up &/or short cycling when pumping down.

    remember pressure means nothing, it's the temperatures that mean everything, then convert it to pressure to achieve required result.
    Setting up switch with dry nitrogen can save a lot of time & more accurate.

    http://www.achrnews.com/articles/874...mpdown-systems
    Last edited by RANGER1; 17-02-2016 at 09:51 AM.

  4. #4
    Join Date
    Feb 2016
    Location
    Australia
    Posts
    2
    Rep Power
    0

    Re: Pressure switch set up

    Thank you, is the cut in temperature measured in relation to the saturation temperature as room reaches temperature? Or because my desired room temperature is 3oC, just so I can apply this for using different refrigerants e.g r404a.

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Pressure switch set up

    hi steg. no you cannot use this on any type of refrigerant the idea of using r134a as you quoted, you where given the temp/ pressure for that refrigerant you will have to get a p/t chart ( you may require a few of them before you retire) because every gas has its own footprint ( as mikeref) suggested. enjoy your new trade. you will never stop learning( I havent and I have been retired 14 years) all the best = sedgy

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Pressure switch set up

    I'd say about 5psi cut out and about 25psi cut in. If you go too high with the cut in the unit may not start in cold weather.
    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pressure switch set up

    Interesting reading,
    a pump down cycle with a thermostat and a solenoid in the perfect situation is great, straight forward and simple, but walk in chillers are notorious for someone either loading room and /or leaving door open for extended periods. So evaporator turns to ball of snow, so setting on LP control is critical to protect compressor and get an air defrost for a possible snow up.
    Generally I wire control circuit through stat and HP/LP in series, so either or will cycle compressor, then cycle solenoid with compressor start /stop, to avoid liquid migration in off cycle. Some time spent on setting LP setting coresponding to room temp and set LP cut out 3>5 psig below that suction pressure. Compressor stops, solenoid closes and evaporators defrosts and restarts on cut in setting at P/T +5 'C, other wise system cycles on stat if evaporator is operating normally at normal conditions
    Saves a lot of call backs and nuisance frost ups

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Pressure switch set up

    Quote Originally Posted by Magoo View Post
    Interesting reading,
    a pump down cycle with a thermostat and a solenoid in the perfect situation is great, straight forward and simple, but walk in chillers are notorious for someone either loading room and /or leaving door open for extended periods. So evaporator turns to ball of snow, so setting on LP control is critical to protect compressor and get an air defrost for a possible snow up.
    Generally I wire control circuit through stat and HP/LP in series, so either or will cycle compressor, then cycle solenoid with compressor start /stop, to avoid liquid migration in off cycle. Some time spent on setting LP setting coresponding to room temp and set LP cut out 3>5 psig below that suction pressure. Compressor stops, solenoid closes and evaporators defrosts and restarts on cut in setting at P/T +5 'C, other wise system cycles on stat if evaporator is operating normally at normal conditions
    Saves a lot of call backs and nuisance frost ups
    Magoo, so no real pump down with this scenario!
    Would it have to have a suction slop pot for this setup?
    Otherwise possible slug back or carryover of liquid!

  9. #9
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Pressure switch set up

    Quote Originally Posted by monkey spanners View Post
    I'd say about 5psi cut out and about 25psi cut in. If you go too high with the cut in the unit may not start in cold weather.
    That is true Jon. In this case, i chose an LP reset pressure higher than 30 Psig because somewhere down the track,an iced evaporator has a hard time raising suction pressure beyond 30-32 Psi when the solenoid kicks in.

    This setting gives the Evaporator some extra time to clear itself of Ice.
    Liquid flooding after LLSV has opened? A suction accumulator. Heatcraft have moved away from the Conventional pump down. Both Compressor and LLSV shut down on the off cycle.
    NO Pump Down.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pressure switch set up

    You don't really need pumpdown, as mikeref said, let compressor and SV shot at the same time, make sure it installed close to the TXV to avoid excess liquid in the evaporator.