Octopush Technology Controller 8320-220V Parameter List
Grup Sıra
Parametre
Birim
Min Max Default
Fan
1
frc
Y/N
No
Yes
No
Fans on with the compressor
2
fst
°C
-55
110
15
Fans stop upper limit
3
Fdf
°C
0.1
10.0
3.0
Fans differential
Cpr
4
Cdf
°C
0.1
10.0
3.0
Differential
5
Scd
min
0
10
1
Compressor delay after start up
6
Sad
min
0
10
1
Delay for compressor switch on
7
Hst
°C
-55
110
15
Maximun allovable temperature
8
Lst
°C
-55
110
-10
Minimun allovable temperature
Dfr
9
Dft
°C
0
100
25
Defrost end temperature
10
Ddu
min
1
60
35
Maximum defrost time
11
Dt
NDF / HG / AIR / EL
0
3
3
Defrost type :0: No defrost /1: Hot gas/2 Off cycle/ 3:Heater elements
12
Sdd
hr
0
24
1
Defrost delay on start up 0: Defrost cancelled
13
Dit
h
1
24
6
Defrost interval.
14
Dct
Ct/Rt
0
1
1
Defrost interval/: 0: Compressor on time /1: Real time
15
Drt
min
1
10
10
Drip time after defrost
Alr
16
Hrt
°C
1
10
3
High temperature alarm
17
Rtd
min
1
240
30
High temperature alarm delay
18
Lrt
°C
1
10
-3
Low temperature alarm
19
Ad
min
1
240
180
Alarm delay at start up
20
Dad
min
1
240
60
Alarm delay after defrost
Cfg
21
Set
°C
Lst
Hst
-5
Set temperature.
22
Tpc
°C
-12.8
12.8
0
Room sensor calibration
23
Epc
°C
-12.8
12.8
0
Evaparator sensor calibration
24
Out
Vers
0
0
20
Octopush Version
25
Adr
Adres
0
254
1
RS485 com address
Dsp
26
Tsd
0/0,0
No
Yes
Yes
Display resolution: Integer / Decimal
27
Dts
def/set/t
0
2
0
Display during defrost: Def / Set valuei / Room temperature
28
Ptd
t/e/c
0
2
0
Temperature displayed: Room / Evaporaor / Condenser