    Carrier Prodialog - How to Isolate Circuit / Comp Through Service Menu



    Carrier 30RB522 / Serial RBJ1409

    Can one assist with a break down of the service menu accessed by password 88. In particular we would like to isolate a circuit pending repair while continuing to operate at 50% load.

    Cheers from down under



  2. #2
    Join Date
    Oct 2009
    Location
    Norway
    Posts
    39
    Rep Power
    0

    Re: Carrier Prodialog - How to Isolate Circuit / Comp Through Service Menu

    is it a circuit a and b? if so, you can just make an alarm for the system you dont want to run.

    I dont think its possible to enable/disable a circuit if its the grey prodialog.

  3. #3
    Join Date
    Jul 2012
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Carrier Prodialog - How to Isolate Circuit / Comp Through Service Menu

    You could unplug the contactor from the PCB next to each compressor then plug it back in when you're done