    thermodynamic panels position



    Hello can anyone help we need to install these panels vertical and the company say the connection of liquid and suction needs to be at the top I think it needs to be at the bottom we are installing 12 black panels so it needs to work correct for heat pump what is heating 9 radiators



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: thermodynamic panels position

    If you have connections at the bottom how do you vent the panels?

    Manufacturer knows best.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: thermodynamic panels position

    Can you explain the vent these are refrigeration panels with liquid and suction on

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: thermodynamic panels position

    Okay, my mistake, I did not realise that they contained refrigerant.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    745
    Rep Power
    25

    Re: thermodynamic panels position

    When we installed these I understood that the connections were at the top when installed vertical so that you didn't suck liquid down your suction. Same reason that when installed horizontally liquid bottom, suction top.
    Which make are you installing?

    Eggs

  6. #6
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: thermodynamic panels position

    I am installing energy panel both liquid and suction come out the same area on the panel even the company is not sure asked other people and there not sure myself I thought the bottom

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: thermodynamic panels position

    .

    If you are given the choice then suction would always be at the highest point,
    but it depends on how the oil is returned? If the oil is trapped and passed
    down the suction with the refrigerant, it would make little difference, if there
    is no provision for getting the oil out of the evap, then it will rely on gravity
    to an extent and positioning of the pipes would be critical.

    Does the evap look like a large version of a domestic fridge evap? A pressed
    Aluminium thing that is then just painted black?

    If it is, then I imagine the positioning of the pipes is not that critical.

    But all said and done the manufacturer should know best and if you do
    not follow their instructions you might void the warranty.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: thermodynamic panels position

    Just follow the manufacturer's instructions, this will guarantee responsibility in case something goes wrong.