    Soft start semi hermetic compressors



    Hi. Is it possible to soft start a 3 phase semi-hermetic compressor? Or does the load (gas pressure) make it impossible?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Soft start semi hermetic compressors

    There is always pressure on the discharge side and there are no problems with soft start, set it not more than 700ms.

    Carlo Gavazzi are making good soft starters for refrigeration compressors at set rump up time, i use them mainly on scrolls over 7.5 HP.
    https://www.gavazzionline.com/motor_controllers.htm

  3. #3
    Join Date
    Aug 2010
    Location
    Portugal
    Age
    38
    Posts
    29
    Rep Power
    0

    Re: Soft start semi hermetic compressors

    Also good for recip?
    What about those with part winding, like some bitzers?
    Last edited by nandoanalog; 23-01-2016 at 08:34 PM.

  4. #4
    Join Date
    Jun 2001
    Location
    Chicago Il
    Age
    52
    Posts
    98
    Rep Power
    23

    Re: Soft start semi hermetic compressors

    copeland has a designed VFD for their 3 phase discus line. Never seen one on a recip but i'd use it.Part wind starting is eliminated as your VFD or soft start will lower your starting amps.

  5. #5
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Soft start semi hermetic compressors

    Shouldn't be any problem at all.

    Just make sure to size the soft starter to suit your application and take into account the higher start current after standstill. *EDIT* (spoke to my electrician friend and he said choose a soft starter that is the next size up from the one that fits the motor Kw to save yourself a lot of headache, and also the specify that you need one designed for a "heavy start") *EDIT*
    Altivar and Danfoss makes good soft starters in my opinion

    On one system I have been on, the customer hired an electrician to replace the star/delta starter with a soft starter, and he had measured the amps the motor was pulling while it was running at normal operating pressures and choose a soft starter to fit that power consumption.

    After installing it he got it running with the help of the on site engineer, but after that it kept stalling (before the holding contactor could take over) after every defrost (cold room at +3C) when the suction pressure would rise.

    It took a whole day of playing with ramping times and start current settings, while running defrost cycles and testing what the highest suction pressure it could manage was.

    If you are considering a soft starter, you should also look into the cost of getting a VFD instead, prices don't differ that much and a VFD gives you more options for compressor regulation.
    Last edited by Tycho; 29-03-2016 at 04:51 PM.