Chiller PRV query
Hi all,
Could anybody please advise if there is a legal requirement in the UK for chillers to be fitted with PRV's? The chillers in question are liquid to liquid reversible units which DO NOT have receivers in them. There are 2 circuits inside the units running on R410a, any advice would be greatly appreciated!
Thanks
-
22-01-2016, 01:16 AM #2
Re: Chiller PRV query
Hi Oceanlab,
standard anywhere is if HX or vessel containing refrigerant can be isolated with valves then said vessels have to have safety relief valves set to vessel design pressure/temperature maximum rating.
-
25-01-2016, 09:00 PM #3
Re: Chiller PRV query
Thanks Magoo, there are no isolation valves anywhere on these units, so I guess they are ok running without PRV's then
-
27-01-2016, 08:39 PM #4
Re: Chiller PRV query
Oceanlab
All pressure systems in the UK fall under the Pressure Directive Regulations if they operate above 0.5Bar. PRV's are mandatory and must be replaced on a regular basis...
Here's a link to some relevant information http://www.hse.gov.uk/pressure-systems/law.htmLast edited by frank; 03-02-2016 at 09:12 PM. Reason: typo
-
27-01-2016, 09:32 PM #5
Re: Chiller PRV query
Thanks you Frank, that makes interesting reading. I am going to contact the company pressure systems AE tomorrow and bring this to his attention