    Chiller PRV query



    Hi all,

    Could anybody please advise if there is a legal requirement in the UK for chillers to be fitted with PRV's? The chillers in question are liquid to liquid reversible units which DO NOT have receivers in them. There are 2 circuits inside the units running on R410a, any advice would be greatly appreciated!

    Thanks



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Chiller PRV query

    Hi Oceanlab,
    standard anywhere is if HX or vessel containing refrigerant can be isolated with valves then said vessels have to have safety relief valves set to vessel design pressure/temperature maximum rating.

  3. #3
    Join Date
    Jan 2015
    Location
    England
    Posts
    15
    Rep Power
    0

    Re: Chiller PRV query

    Thanks Magoo, there are no isolation valves anywhere on these units, so I guess they are ok running without PRV's then

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Chiller PRV query

    Quote Originally Posted by Oceanlab View Post
    Hi all,

    Could anybody please advise if there is a legal requirement in the UK for chillers to be fitted with PRV's? The chillers in question are liquid to liquid reversible units which DO NOT have receivers in them. There are 2 circuits inside the units running on R410a, any advice would be greatly appreciated!

    Thanks
    Oceanlab

    All pressure systems in the UK fall under the Pressure Directive Regulations if they operate above 0.5Bar. PRV's are mandatory and must be replaced on a regular basis...
    Here's a link to some relevant information http://www.hse.gov.uk/pressure-systems/law.htm
    Last edited by frank; 03-02-2016 at 09:12 PM. Reason: typo

  5. #5
    Join Date
    Jan 2015
    Location
    England
    Posts
    15
    Rep Power
    0

    Re: Chiller PRV query

    Thanks you Frank, that makes interesting reading. I am going to contact the company pressure systems AE tomorrow and bring this to his attention