16-01-2016, 12:00 AM #1
Condenser failed!
A tube on a water cooled condenser failed. What I thought to be a 5 minute job, is turning into a challenge, to say the least.... No matter what, I can't heat the thing enough to braze, nor soft solder! Even with a cutting torch!
I'm thinking about plugging both ends with steel, and arc weld them! Feels silly....
Sugestions?
-
16-01-2016, 12:40 AM #2
Re: Condenser failed!
Assuming tubes are expanded copper, usually you can use a tapered pin, hammer in, check for leaks,
or you can buy special tube expander roller to re-expand tube,
or drill out tube, tap in thread & screw in plug with thread sealant
https://m.youtube.com/watch?v=LsfRQGm4-Lc
http://www.tcwilson.com/heat_exchanger/tube_expander/Last edited by RANGER1; 16-01-2016 at 12:50 AM.
-
16-01-2016, 06:05 AM #3
-
16-01-2016, 07:46 AM #4
Re: Condenser failed!
Close damaged tube in both ends by conical plugs. Use hummer but do it gently, don't destroy end plate.
Good luck.
DSC00317.JPG
-
16-01-2016, 10:20 AM #5
Re: Condenser failed!
A Good Post Alex.
Thanks for taking the time to source a photo of a plug being used.
Most informative for those that do not Know.
And one of the options Ranger was advocating.
GrizzlyDespite the High Cost of Living it still remains Popular!
-
16-01-2016, 12:21 PM #6
-
16-01-2016, 06:03 PM #7
Re: Condenser failed!
10 out of 10! For our Russian colleagues Input!
GrizzlyDespite the High Cost of Living it still remains Popular!
-
18-01-2016, 01:53 AM #8
Re: Condenser failed!
Please do not heat-up or try to blaze or weld the tube sheet, as this will cause leakage to other pipes around that area.
Those condenser tubes were rolled and expanded to the tube sheet, heating up will loosen the joint.
-
18-01-2016, 08:22 AM #9
Re: Condenser failed!
Actually thinking I should do the job properly, and replace the tube instead!
-
18-01-2016, 08:32 PM #10
Re: Condenser failed!
You may not be able to, as a lot of the time condensers have heat transfer fins on
tubes.
It can also start to be a project you were not looking for.
Plug it off is my advice.
-
20-01-2016, 12:42 AM #11
Re: Condenser failed!
Hi nandoanalog
I am with Ranger on this one, I have used tapered pins and also tapped a thread but in both cases use some sort of sealer, leaklock or loctite.
Also iwan seltech makes a good point about not heating the end plates, as you have already done this you may want to check all the tubes for leaks after sealing the damaged tube.
PaulBorn to fish, forced to work
-
20-01-2016, 01:10 AM #12
Re: Condenser failed!
Hi
totally agree with previous posters. Heating tube sheet will create a bigger project than you would imagine.
There are two piece brass plugs available for blanking tubes each end. You can reduce tube bundle by max 10% of what is installed without creating too many issues.
Replacing a condenser tube is not a big issue if you have the right tools. ( tools expensive though )
The condenser tube will be internally expanded at baffle plates as well .Better to blank off failed tube.
-
20-01-2016, 05:14 AM #13
Re: Condenser failed!
I ordered some plugs, and a tube expander roller tool to fix this one.
I'm still interested in at least learning how to retube condensers, as just yesterday I found out that nobody does that in my country! They'll just change the whole thing... The largest hvac supplier didn't even know what a tube expander roller was.
I've been watching some heat exchanger making videos, and some guys braze the tubes to the baffle plates! I wonder if a tube puller would pull a brazed tube???
-
20-01-2016, 05:15 AM #14
Re: Condenser failed!
BTW, many thanks to all the posters!!! I little help goes a long way!
-
21-01-2016, 10:14 AM #15
-
21-01-2016, 10:52 PM #16
-
22-01-2016, 04:51 AM #17
Re: Condenser failed!
Sea water!! That's why!
-
05-02-2016, 07:27 PM #18
Re: Condenser failed!
May i ask if the innstallation is on a ship or rig? they usual have ten times the max water flow through condenser :P
-
02-03-2016, 02:51 PM #19
Re: Condenser failed!
whats the best way to go about a condenser full of seawater? get all the sea water out with vac pump, flush it with fresh water plug the tube and then vac it out then tripple evacuate with nitro?