    Angry Mitsubishi



    I have a system with 10 indoors and 3 lossnay units and 1 ae200.
    each lossnay unit is on a different floor.
    when I connect the lossnay units to the mnet I am getting the dreadful 6607 fault.
    system works with only one lossnay connected but when I connect the other two it goes into fault.
    the lossnay units are not interlocked with any indoor.
    do you still have to set the main/sub switch on the other two lossnay units even though they are on differant floors?



  2. #2
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Mitsubishi

    Have you addressed the lossnays? They should be the last 3 addresses on the system. Have you entered the addresses into the AE200?