    mitsubishi fdc200vs no heat



    His guys.dont know whether you can help.i was called out to a fdc200vs multi split which the customer says there's no heat.started it up on heat and the compressor runs for 30 seconds and shuts off.if I switch it to cooling the pressure in the suction line pulls straight down to 4 bar and shuts down.if I switch the mains off you can hear what sounds like a valve opening and gas feeding.when it stops the controller shows the sun and a hand and shortly after the controller shuts off and the red light flashes. anyone have any ideas.thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: mitsubishi fdc200vs no heat

    have you checked the gas charge? 410 system should be 8 bar, interogate hp ,lp alarms have to alarm a few times to generate a fault code- check the remote controller for operation data, will tell ya sensor values and comp current, comp freq
    if its a cassette sometimes have issues with hi condensate float switch sticking, also filter door switchs fail too

  3. #3
    Join Date
    Feb 2015
    Location
    england
    Posts
    1
    Rep Power
    0

    Re: mitsubishi fdc200vs no heat

    hi
    what about on cooling mod ? same problem u having ?