    Hiya.
    This year we have fitted quite a few soft starts.
    faults ranging from tripping the mcb on start, nearly going on fire, burning out and capacitor inside leaking fluid.
    Common starter is fitted throughout the Delonghi range
    Carlo Gavazzi 32a





    Any one else had problems?
    Any better ones to get?



  2. #2
    Join Date
    Feb 2014
    Location
    UK
    Posts
    26
    Rep Power
    0

    Re: Carlo Gavazzi soft starts fitted to Delonghi Heat Pumps

    Only comment I can make is that I note that Danfoss have stopped using these and install the Emerson CSS units instead as replacements.

  3. #3
    Join Date
    Mar 2007
    Location
    manchester
    Age
    17
    Posts
    63
    Rep Power
    19

    Re: Carlo Gavazzi soft starts fitted to Delonghi Heat Pumps

    Yes, had similar experience on a York packaged unit. Burned out and popped