    Daikin vrv iv



    Hi everyone,

    just need a bit bit of technical intellect, first time commissioning a vrv Iv and after addressing the system I found the lads had wired the new multi boxes up wrong on the slaves on put them in the bs unit connection rather than outdoor unit side, anyway to cut a story shut after re wiring and restarting the fault remains on both systems after looking for the old faithful reset button in the condenser I've noticed it's now gone and been replaced with just 3 buttons, is there still a way of doing a hard restart does anyone know for when I'm back in the morning? It'll save me an hours tech call if someone could help me out.

    thanks



  2. #2
    Join Date
    Mar 2014
    Location
    England
    Posts
    32
    Rep Power
    0

    Re: Daikin vrv iv

    Quote Originally Posted by and1dude2001 View Post
    Hi everyone,

    just need a bit bit of technical intellect, first time commissioning a vrv Iv and after addressing the system I found the lads had wired the new multi boxes up wrong on the slaves on put them in the bs unit connection rather than outdoor unit side, anyway to cut a story shut after re wiring and restarting the fault remains on both systems after looking for the old faithful reset button in the condenser I've noticed it's now gone and been replaced with just 3 buttons, is there still a way of doing a hard restart does anyone know for when I'm back in the morning? It'll save me an hours tech call if someone could help me out.

    thanks
    Enforce a re-initialization of communication: hold push button BS3 “return” for minimum 5
    seconds.

  3. #3
    Join Date
    Jan 2008
    Location
    derbyshire
    Posts
    15
    Rep Power
    0

    Re: Daikin vrv iv

    Quote Originally Posted by Asbolute View Post
    Enforce a re-initialization of communication: hold push button BS3 “return” for minimum 5
    seconds.
    Thanks mate, do I need to power the indoors down while doing that or can I just fire away and go for it in its current in fault condition?

  4. #4
    Join Date
    Aug 2009
    Location
    Dartford
    Age
    34
    Posts
    88
    Rep Power
    15

    Re: Daikin vrv iv

    Just fire away mate. I always turn the controllers off but that's just me

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin vrv iv

    How can you turn the controllers off on a Daikin vrv?

  6. #6
    Join Date
    Aug 2009
    Location
    Dartford
    Age
    34
    Posts
    88
    Rep Power
    15

    Re: Daikin vrv iv

    Just press the on off button? I only turn them off as it's a mind thing, it probably don't make a difference but to me it does lol
    Last edited by Deano240; 10-01-2016 at 10:38 AM.

  7. #7
    Join Date
    Apr 2002
    Location
    scotland
    Posts
    114
    Rep Power
    23

    Re: Daikin vrv iv

    I've been having quite a few issues with these IV's lately, mostly blown PCB's and fan motors, I'm getting a little concerned about the build quality, at the moment though all parts covered under D5