Results 1 to 12 of 12
    ghil's Avatar
    ghil Guest
    Refrigerant 410A
    Hello to all members,
    please give me information about 410A v R22.
    We are charging R22 in 1.5 ton air conditioning unit about 60-70 pound what about air condition like 410A how much refrigerant required in pound.
    Jul 2010
    NTH.QLD Australia
    56
    1,757
    27
    Re: Refrigerant 410A
    18,000 Btu A/c on R22 cannot be changed to R410A.
    R410A A/C's suction pressure is much higher. 115 to 120 ish Pounds per Square Inch is basically the normal under load conditions.
    Aug 2014
    43
    R22 to R410a is not compatible
    i have been doing R22 to R438A with an oil additive and so far have been successful with no known issues with systems operating for the last 4-6 months
    Feb 2016
    Belize
    1
    I have been out of the country for 10 years now. I haven't been really keeping up with the information. Where I am here in Belize, Mini Splits are the norm and very little of that. It's a poor country so not much of it. My question is this. I have a customer with a 5 ton Nordyne R-22. We live on the beach so the outside unit is in bad shape. I want to replace the outside unit with an R-410-A condenser. Providing the check flow regulator is the same, will the system operate with the new piston provided as long as I flush the evap coil and lines. Has anyone had experience with this. This is all new Technology here lololol and I was to retire here but they found out what my profession was. Thanks
    Somerset
    64
    4,587
    Rather than repeat and adding to what fellow engineers have already said.
    Just watch this Video!
    https://www.youtube.com/watch?v=qxwcVKjJuSQ
    Are you going to get the customer to sign a disclaimer? so should any of the components fail you cannot get sued?
    If you don't know most of the issues discussed you certainly are not going to (I assume?) have the correct equipment designed to work on R410a.
    Trust me the Pressures in a R410a system are 60% higher than R22.
    Here in the UK we will pressure test a new system to approx. 675psi to accommodate our Highest average ambient temperature.
    The loading in Belize will be way above that, never mind he 80% Humidity!
    Don't miss the part about Mineral Oils and POE Oils!
    Feb 2014
    Canada
    1
    R-22
    Often referred to by a brand name like *****
    As of 2010, R-22 was discontinued for use in new air conditioning systems
    R-22 is a hydro-chlorofluorocarbon (HCFC) which contributes to ozone depletion
    R-410A
    Often referred to by a brand name like Puron
    Has been approved for use in new residential air conditioners
    Is a hydro-fluorocarbon (HFC) which does not contribute to ozone depletion
    Will become the new standard for U.S. residential air conditioning systems in 2015
    Aug 2014
    South Africa
    35
    26
    I believe he is asking the correct charging pressure for R410a not retrofitting.
    Jan 2006
    Croatia
    2,136
    Hi, ghil
    Quote Originally Posted by ghil View Post
    Here is something interesting:
    http://www.brighthubengineering.com/...rants-for-r22/
    but .... please, check this link too:
    http://www.refrigeration-engineer.co...cement-of-R-22
    Seems some other refrigerants are better replacement for R22 ....
    You can check a lot of other useful things on RE forums .... just need some time ..
    Best regards, Josip
    Jul 2010
    NTH.QLD Australia
    56
    1,757
    27
    Quote Originally Posted by Recoilzn View Post
    I believe you are right. Misread charging for changing. Points going your way.
    A/C's have a specific weight of refrigerant on the outdoor unit Compliance sticker...in Metric.
    May 2016
    New zealand
    407c can replace r22 with a oil changeout too.
    Jun 2011
    Australia
    47
    Quote Originally Posted by mattmechanic View Post
    How has R438A been going for you now and what is the additive. I have a 4kg r22 system and looking at changing to r438a after repair. It has a Copland rotary compressor
    Sep 2003
    ISRAEL
    66
    4,153
    38
    I use for a few years now R438A in various systems - From water chillers to milk cooling units. works fine. TXV adjustment is required some times. No oil change.
    If you work in temp below 0 I would suggest R422D. I use it for cooling units is CO2 tanks at -30C evaporating temp.