    swapping r290 for r404a



    hi there all

    I spoke to a engineer today who swear blind if you have a r290 system you can replace the gas with r404a and it will run the same you dont even have to change the oil or the pot , he says he has done it a few times and the fridges are running fine after a year or so , i mean come on seriously this cannot be right ?



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: swapping r290 for r404a

    .

    404 and 290 have very similar properties, they can and
    do use the same compressor. 404 will be in short demand
    very soon so tell the engineer to get used to 290, it is the
    future.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Dec 2006
    Location
    UK
    Posts
    110
    Rep Power
    19

    Re: swapping r290 for r404a

    Compressors manufactured by Embraco labelled r290 are exactly the same as their equivalent r404a compressors. So yes, you can empty an r290 system and replace it with r404.

    We do the above fairly regularly with the ‘Walls Ice Cream Display Freezers”, which are always blocking out; we empty the system resolve the blockage and recommission with r404.

    I suppose with the current phase down, which will really hurt in 2018, then it will be the other way round. However the rumours in the industry is that r407f is to be the replacement and pretty much the drop in for r404. J&E Hall already advertise most of their r404 systems as compatible with r407f.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: swapping r290 for r404a

    Hi Rob and Rtic.
    Some useful info.
    Thanks.
    Grizzly

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: swapping r290 for r404a

    R290 is used only for environmental reasons, I back Rtic words and add that r404A is a problematic refrigerant.
    I have seen a few units run with R404A where the refrigerant stopped cooling and head pressure went sky high, all components was fine, replacing the charge sorted the problem.
    In a big plant where as an outsource contractor, I look after many low temp units, I have replaced all R404A with R507 and never had a problem since.

    Most manufacturers of small compressors are only making two kinds of compressors, low temp and medium,high ones so if the refrigerants have similar properties, you can change them without any problem of performance.

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,044
    Rep Power
    35

    Re: swapping r290 for r404a

    Quote Originally Posted by chemi-cool View Post
    I have seen a few units run with R404A where the refrigerant stopped cooling and head pressure went sky high, all components was fine, replacing the charge sorted the problem.
    Yes, not that I have witnessed this myself but the chest freezers in Lidl's (or was it Aldi?) would throw a wobbler and this was the cure, replace the R404 and all working again.
    Health and safety first..........unless I'm in a hurry.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: swapping r290 for r404a

    Quote Originally Posted by abp32 View Post
    hi there all

    I spoke to a engineer today who swear blind if you have a r290 system you can replace the gas with r404a and it will run the same you dont even have to change the oil or the pot , he says he has done it a few times and the fridges are running fine after a year or so , i mean come on seriously this cannot be right ?
    Since R290 compressor runs usually on mineral oil, retrofitting R290 to r404A should require same procedure as retrofitting R22 to r404A. That include changing oil to POE type!

    Also, depending on evaporation temperature, with same compressor displacement, according to Coolpack software, capacity increase is 10-20% with use of R404A on same compressor, and therefore, condenser should be checked for sufficient heat rejection capacity!
    Last edited by nike123; 20-12-2015 at 08:53 AM.

  8. #8
    Join Date
    Feb 2015
    Location
    uk
    Posts
    36
    Rep Power
    0

    Re: swapping r290 for r404a

    it must be small fridge he is talking about

  9. #9
    Join Date
    Jun 2013
    Location
    England
    Posts
    14
    Rep Power
    0

    Re: swapping r290 for r404a

    Apologies for picking up an old thread. I read post re: Walls freezers. I have a Foster 2 door bench type freezer on a Danfoss pot that leaked on the return. Designed with 290. Has anyone ever dropped 404 in to one of these smaller applications with positive results. The only issue I see on the smaller hermetic applications is the oil as 404 should be run on no more than 90% charge of polyol ester (as I recall). Any help greatly appreciated. Not a big issue as can grab a canister of 290 but thought it worth asking and for future reference.
    Cheers

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •