    Unhappy PURY-P250YGM-A 1102 fault



    1102 fault driving me mental

    PURY-P250YGM-A
    Indoor units gutted and clean until they shine
    Outdoor unit gutted and cleaned
    correct gas charge in unit
    1102 now appears and then 1302
    compressor going to 112 deg c then ramps down to 75 deg c then up to 112 again (heating)

    any advice?



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: PURY-P250YGM-A 1102 fault

    Quote Originally Posted by spamfish View Post
    1102 fault driving me mental

    PURY-P250YGM-A
    Indoor units gutted and clean until they shine
    Outdoor unit gutted and cleaned
    correct gas charge in unit
    1102 now appears and then 1302
    compressor going to 112 deg c then ramps down to 75 deg c then up to 112 again (heating)

    any advice?

    Don't Gut and Clean em...................



    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Mar 2008
    Location
    Manchester
    Age
    74
    Posts
    33
    Rep Power
    0

    Re: PURY-P250YGM-A 1102 fault

    Check inddor fileter n non condensibles
    The moving finger writes and leaves a broken fingernail behind!

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: PURY-P250YGM-A 1102 fault

    The compressor is going into protection mode due to the high discharge temp. It's a typical sign of overheating and if you don't address it you will lose the compressor.

    I would check the oil level in the compressor with an infra red thermometer. If it's low then add a little oil into the suction line

  5. #5
    Join Date
    Aug 2009
    Location
    Dartford
    Age
    34
    Posts
    88
    Rep Power
    15

    Re: PURY-P250YGM-A 1102 fault

    Is this in heating mode? I would check LEV 3 in the BC box. undo it to see if it's stuck