    Water 300 controller alarm problem



    Hi all ,

    I have problem with Climaveneta chiller/heat pump and the controller

    The machine use Water 300 controller .

    And now shows :
    AL:003 – Evaporator pump thermal protection

    After i reset the alarm manually it shows it again and again .

    Any idea what to do ?



  2. #2
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Water 300 controller alarm problem

    Check pump motor and contactor reset overload check running amps

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Water 300 controller alarm problem

    Could be a thermistor in the pump motor winding.

    See if there extra 2 wires in the motor connection box.