    System ck on carrier maxima 1000



    Any one any ideas why unit randomly shutting down on electric stby " system ck " comes on screen. Charge rate ok. Sensor fault. Any help or guidance much appreciated



  2. #2
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: System ck on carrier maxima 1000

    Usually system ck is caused by suction pressure reading in the negatives for five minutes. Corrosion in the wiring / plug or bad transducer can cause an intermittent code. Could also be discharge air sensor reading higher than return air in cool.

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: System ck on carrier maxima 1000

    Call up the suction pressure on the screen and watch it if it goes negative it will shut down I take it that it's defrosting enough for its load requirements.

  4. #4
    Join Date
    Apr 2009
    Location
    n ireland
    Posts
    13
    Rep Power
    0

    Re: System ck on carrier maxima 1000

    Cheers guys mainly work on Thermo King will check sensors