    Configuring 100% Back up



    Gents,

    I hope you are all well!

    I have been asked to design a refrigeration system to connect to an AHU supplying a food production factory. The client wants 100% back up should the system fail. The AHU has only 1 DX coil but I need to connect 2x 66kw multi compressor packs to it. 1 pack will do the duty whilst healthy and the 2nd pack is to be solely for 100% back up should the 1st pack fail. I am wondering if any of you guys have any ideas as to how we could configure this?

    Obviously we have just one DX Coil and so just 1 refrigerant circuit, to which we need to connect both packs. I am thinking along the lines of motorised ball valves at the pack end to shut off whichever is not in use. My concern is with the refrigerant charge and how much refrigerant could potentially be trapped in the pack which is shut down, leaving the circuit short of gas. If we do not isolate the pack which is not in use then obviously we are likely to fill it up with oil from the other one?!

    Any ideas please would be very much appreciated!!!

    Thank you in advance!



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Configuring 100% Back up

    Quote Originally Posted by NewmanRef View Post
    Gents,

    I hope you are all well!

    I have been asked to design a refrigeration system to connect to an AHU supplying a food production factory. The client wants 100% back up should the system fail. The AHU has only 1 DX coil but I need to connect 2x 66kw multi compressor packs to it. 1 pack will do the duty whilst healthy and the 2nd pack is to be solely for 100% back up should the 1st pack fail. I am wondering if any of you guys have any ideas as to how we could configure this?

    Obviously we have just one DX Coil and so just 1 refrigerant circuit, to which we need to connect both packs. I am thinking along the lines of motorised ball valves at the pack end to shut off whichever is not in use. My concern is with the refrigerant charge and how much refrigerant could potentially be trapped in the pack which is shut down, leaving the circuit short of gas. If we do not isolate the pack which is not in use then obviously we are likely to fill it up with oil from the other one?!

    Any ideas please would be very much appreciated!!!

    Thank you in advance!
    You could always change the DX coil in the AHU for a water/glycol coil then use 2x plate heat exchanges, 1 for each pack so that they are separate refrigeration circuits, and use a shunt pump and sol valves between the PHE's and the AHU coil.
    I would also add a buffer vessel.

  3. #3
    Join Date
    Aug 2001
    Location
    Nr Manchester, UK
    Age
    54
    Posts
    36
    Rep Power
    0

    Re: Configuring 100% Back up

    Surely you will still have a common point of failure in the single coil. Wouldn't it all fail in the event of a coil failure?

    I would say it isn't 100% backup unless there were two complete systems

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Configuring 100% Back up

    Evaporator coil failure is less likely than a refrigerant leak or expansion valve failure, which would affect either of the systems.
    Suggest as others that you have a twin circuit evaporator coil, thereby eliminating the common failure factor.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  5. #5
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Configuring 100% Back up

    you need two seperate systems to have 100% backup

  6. #6
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Configuring 100% Back up

    Quote Originally Posted by martinw58 View Post
    you need two seperate systems to have 100% backup
    Agreed two separate systems is the only way,I built an freezer room recently with two systems the only thing that's common is the incoming power supply to the whole building .

  7. #7
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Configuring 100% Back up

    Simpler idea would be to use a single larger condenser pack with step / stage control and multiple compressors. As you only have a single refrigerant circuit in your initial idea you are not going to cover this with both the designs but cost and simplicity is better.
    I love the smell of Ammonia in the morning!