    I'm building a small 1/2ton system with a pump down cycle, Now I've been wondering where the ideal placment would be for the NC Valve, I'm thinking the best would be close to the TVX as possible to keep the liquid line flooded. Does this sound like a good Idea?

    Right now there are no fixed numbers, I'm just building the basic frame work and part possitions.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Ideal Solinoid valve placment?

    With the NC valve close to the TXV you will reduce vibration and possible liquid hammer inside the pipework when the valve opens releasing a slug of high pressure liquid.

    A long run after the NC can create problems such as those above, it will also make your pumpdown take longer as the liquid has to pass through the TXV etc.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Ideal Solinoid valve placment?

    I'm building a small 1/2ton system with a pump down cycle, Now I've been wondering where the ideal placment would be for the NC Valve, I'm thinking the best would be close to the TVX as possible to keep the liquid
    line flooded. Does this sound like a good Idea?

    Yes. Also, be sure to place it in a serviceable position.

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Ideal Solinoid valve placment?

    Ya thats what I was thinking, it will reduce alot of things in a good way by placing it inches away from the TXV rather then at the plant its self, and at the plant have a manual Valve that is hand opperated right after the receiver to enable service of the TXV, Valve, Sight Glass, Filter dryer.

    So: Conedencer > Receiver > Hand Valve (NO) > Filter/Dryer > Sight Glass > ~?distance?~ > Solinoid Valve (NC) > ~ a fiew inches but no more then a foot ~ > TXV.

    That sound good? This will run paralell to the suction line and be Insulated well.

    and as to whether it is a good idea or not is what I'm asking lol but I imagin that a liquid line aut to be flooded with liquid? would it not?

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Ideal Solinoid valve placment?

    Oh and don't worry I all ways design every thing super easy to service, drives me nuts how some make some thing that is near impossible to assemble let alone fix should it fail!

    I find if you build it logical and throughly Analise your design with a common sense out look it will all ways come out as robust and reliable yet easy to fix and maintain

Similar Threads

  1. Scotsman commercial H2O inlet valve
    By fullcourt in forum Trouble Shooting
    Replies: 9
    Last Post: 25-04-2006, 11:41 PM
  2. 134a expansion valve question
    By g_norman in forum Technical Speculations
    Replies: 3
    Last Post: 18-03-2006, 03:06 AM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •