Costan FAB 7232
Hi folks - I need to select a condensing unit for a 3m Costan FAB 7232 dairy case. There is no available information on the currently installed condensing unit or the compressor (all labels have been removed) - any ideas on the case load or how to select the unit required??
Regards to all..
-
18-11-2015, 07:52 PM #2
Re: Costan FAB 7232
Size of condenser and TXV capacity will help you.
Refrigerant type is written on top of the TXV.
-
19-11-2015, 08:08 PM #3
Re: Costan FAB 7232
very hard at times to get basic info, any idea how old this cabinet is?
Mostly found in the southern part of this green and pleasant land.
-
19-11-2015, 09:09 PM #4
Re: Costan FAB 7232
try here:
http://www.costan.com/
-
25-11-2015, 12:18 AM #5
-
25-11-2015, 11:49 PM #6
Re: Costan FAB 7232
I guesstimated at 4000w@-5 evaporating based upon cabinet display volume, using current data supplied by other manufacturers websites. I also emailed Costan directly who did come up with the cabinet installation manual and data sheet from 1989! Cooling load is 3800-4500watts dependant on required case temperature. The reason for the question was that I went to a service call with a cabinet running continually, not acheiving temperature, the condensing unit has been butchered and has had a small footprint compressor fitted that was clearly too small and not original item, the display temp air off was reading +3, but upon checking found to be +10! Whoever fitted the compressor also put a -6 degree offset on the eliwell controller. I have advised the customer that a new unit is required.