    Costan FAB 7232



    Hi folks - I need to select a condensing unit for a 3m Costan FAB 7232 dairy case. There is no available information on the currently installed condensing unit or the compressor (all labels have been removed) - any ideas on the case load or how to select the unit required??
    Regards to all..



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Costan FAB 7232

    Size of condenser and TXV capacity will help you.
    Refrigerant type is written on top of the TXV.

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Costan FAB 7232

    very hard at times to get basic info, any idea how old this cabinet is?
    Mostly found in the southern part of this green and pleasant land.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Costan FAB 7232


  5. #5
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: Costan FAB 7232

    I was laughing. You are right...OR orifice size OR size of Compressor will give you cooling load and gas.
    Here is no need to hunt down Costan. Just switch brains on.


    Quote Originally Posted by chemi-cool View Post
    Size of condenser and TXV capacity will help you.
    Refrigerant type is written on top of the TXV.

  6. #6
    Join Date
    Nov 2005
    Location
    wales
    Posts
    66
    Rep Power
    20

    Re: Costan FAB 7232

    I guesstimated at 4000w@-5 evaporating based upon cabinet display volume, using current data supplied by other manufacturers websites. I also emailed Costan directly who did come up with the cabinet installation manual and data sheet from 1989! Cooling load is 3800-4500watts dependant on required case temperature. The reason for the question was that I went to a service call with a cabinet running continually, not acheiving temperature, the condensing unit has been butchered and has had a small footprint compressor fitted that was clearly too small and not original item, the display temp air off was reading +3, but upon checking found to be +10! Whoever fitted the compressor also put a -6 degree offset on the eliwell controller. I have advised the customer that a new unit is required.
    Thanks for the replies...