    Daikin VRV-S refrigerant leak



    This is a Daikin VRV-S II installed in 2008, model number RXYMQ48MVJU connected to four indoor ducted units FXSQ-M. This is the first problem with this system since installation.

    Unit tripped out on F3 - High discharge temp. After checking t-misters and such found the unit low on gas (total charge is 15.3Lbs found loss of 2.9Lbs). Inspected all flair connections and refnet branches to see if there was evidence of trace oil from a leak, but nothing showed. Used a refrigerant sniffer around outdoor unit coil and piping and all indoor unit coils. Sniffer did not detect any leaking refrigerant.

    I have done a search on the forum for likely refrigerant leak points on this equipment. While I have found lots of information on other Daikin models that have leak problems, I have not found much on this equipment.

    I am hoping someone with experience on this model of equipment can suggest other likely areas that may leak.

    Thank you.



  2. #2
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Daikin VRV-S refrigerant leak

    Did you pressure test with ofn , when all the gas was reclaimed from the system?
    I like to separate the out door side of the system from the indoor.
    Put 15 bar into the outdoor on a gauge and hose, shut the service ports and then put gauge on indoor side. And take to 20 bar. And wait 24 hours.
    Yes service ports. Can leak back , but I've found that rare.
    You may find. One side is. Down .
    It would seem to be a small leak as you have not lost much gas , over the six years.
    All so you could try a bubble test on the flares, may not show at first glance.
    But wait, and see if you get that tiny blip.
    Some refrigerant can hide under the oil in the compressor
    Good luck.

  3. #3
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S refrigerant leak

    Quote Originally Posted by still learning View Post
    Did you pressure test with ofn , when all the gas was reclaimed from the system?
    I like to separate the out door side of the system from the indoor.
    Put 15 bar into the outdoor on a gauge and hose, shut the service ports and then put gauge on indoor side. And take to 20 bar. And wait 24 hours.
    Yes service ports. Can leak back , but I've found that rare.
    You may find. One side is. Down .
    It would seem to be a small leak as you have not lost much gas , over the six years.
    All so you could try a bubble test on the flares, may not show at first glance.
    But wait, and see if you get that tiny blip.
    Some refrigerant can hide under the oil in the compressor
    Good luck.
    Thank you still learning for your thoughts. No, we have not yet isolated the indoor from the outdoor and pressurized them individually. We'll start with bubbles on the flairs.

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Daikin VRV-S refrigerant leak

    If the system is still operational, you could try adding a small quantity of leak detection dye.
    Let the system run for a period of time, maybe an hour or so and then use the UV lamp to check for leaks.
    This may help you to speed up locating the leak.
    If it has only lost a small quantity over a relatively long period of time it can sometimes be difficult to find the leak, or it could be that the leak has only recently occurred and is losing refrigerant at a rate that can be detected.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  5. #5
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S refrigerant leak

    Quote Originally Posted by hyperion View Post
    If the system is still operational, you could try adding a small quantity of leak detection dye.
    Let the system run for a period of time, maybe an hour or so and then use the UV lamp to check for leaks.
    This may help you to speed up locating the leak.
    If it has only lost a small quantity over a relatively long period of time it can sometimes be difficult to find the leak, or it could be that the leak has only recently occurred and is losing refrigerant at a rate that can be detected.
    We have been operating under the assumption that the leak is recent. Prefer not to use UV dye if possible and the reason we were hoping to find out the most likely places for a leak to occur on this particular equipment. Thanks for your comments.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin VRV-S refrigerant leak

    Check also where pipework may be rubbing against hard supports etc.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Daikin VRV-S refrigerant leak

    I had to look at a google image of a vrv s.
    If it is. A twin fan looking like a split outdoor unit, I would look behind the compressor and up and down the coil , quite hard to see,dakin had a bit of a problem. With outdoor coils at one point.
    Sometimes you can run your finger thru one of the drain holes in the bottom pan of The outdoor and feel oil mist residue.

  8. #8
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S refrigerant leak

    Quote Originally Posted by Brian_UK View Post
    Check also where pipework may be rubbing against hard supports etc.
    Thanks Brian. When I did the site search I found and read about the RZQ models and the consistent problem with pipe work rubbing on the frame on the outdoor unit. Is this the same issue you are suggesting we look for?

  9. #9
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S refrigerant leak

    Quote Originally Posted by still learning View Post
    I had to look at a google image of a vrv s.
    If it is. A twin fan looking like a split outdoor unit, I would look behind the compressor and up and down the coil , quite hard to see,dakin had a bit of a problem. With outdoor coils at one point.
    Sometimes you can run your finger thru one of the drain holes in the bottom pan of The outdoor and feel oil mist residue.
    I think this is same issue Brian suggested - no? Does this require coil replacement or is it typically repairable?

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin VRV-S refrigerant leak

    I don't know of coil problems with VRV's but I have had pipework leaks due to expansion and contraction rubbing pipes against heard corners, pipe trays etc.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S refrigerant leak

    Quote Originally Posted by Brian_UK View Post
    I don't know of coil problems with VRV's but I have had pipework leaks due to expansion and contraction rubbing pipes against heard corners, pipe trays etc.
    Got it - thanks.

  12. #12
    Join Date
    Mar 2014
    Location
    England
    Posts
    32
    Rep Power
    0

    Re: Daikin VRV-S refrigerant leak

    Quote Originally Posted by mchild View Post
    This is a Daikin VRV-S II installed in 2008, model number RXYMQ48MVJU connected to four indoor ducted units FXSQ-M. This is the first problem with this system since installation.

    Unit tripped out on F3 - High discharge temp. After checking t-misters and such found the unit low on gas (total charge is 15.3Lbs found loss of 2.9Lbs). Inspected all flair connections and refnet branches to see if there was evidence of trace oil from a leak, but nothing showed. Used a refrigerant sniffer around outdoor unit coil and piping and all indoor unit coils. Sniffer did not detect any leaking refrigerant.

    I have done a search on the forum for likely refrigerant leak points on this equipment. While I have found lots of information on other Daikin models that have leak problems, I have not found much on this equipment.

    I am hoping someone with experience on this model of equipment can suggest other likely areas that may leak.

    Thank you.
    I'd be surprised if you'd get F3 high discharge with a loss of 1kg from 7kg of gas. Are you sure there is not a refrigerant flow issue?

  13. #13
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S refrigerant leak

    Quote Originally Posted by Asbolute View Post
    I'd be surprised if you'd get F3 high discharge with a loss of 1kg from 7kg of gas. Are you sure there is not a refrigerant flow issue?
    No, not sure there isn't a flow issue. Since low gas can cause high discharge temp, when we found it low on gas we assumed that was the reason for the F3 code. At this point the F3 code has only occurred that one time and the unit is operating continuously after correcting the charge level. We will be undertaking the leak search in the next few days and once that has been corrected then we will see if there are any other operating issues. Thanks for the heads up on that.

  14. #14
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Daikin VRV-S refrigerant leak

    I see what Brian means by hard supports.
    and the corner of the coil behind the compressor is always worth a look , as there have been. Failures in the past, and yes the whole coil was replaced, on r z q models.
    We only ever had four of your type of unit on one site and have only replaced a couple of fans And some boards I think .

  15. #15
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S refrigerant leak

    Quote Originally Posted by still learning View Post
    I see what Brian means by hard supports.
    and the corner of the coil behind the compressor is always worth a look , as there have been. Failures in the past, and yes the whole coil was replaced, on r z q models.
    We only ever had four of your type of unit on one site and have only replaced a couple of fans And some boards I think .
    Well, it is good to hear that overall the equipment is fairly well built. Just have to now locate that leak.

  16. #16
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Daikin VRV-S refrigerant leak

    On older VRV's (talking 10yrs, R407C) have seen the expansions valves leaking on indoor and outdoor units. If the leak detector goes off inside the unit, assuming you can get in there well enough then unscrew the head then you can see bubbles with leak spray. Outdoor EEV's bit simpler to check.

    Not sure how this applies to newer models but thought worth a mention.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  17. #17
    Join Date
    Oct 2007
    Location
    United States
    Posts
    213
    Rep Power
    17

    Re: Daikin VRV-S refrigerant leak

    Quote Originally Posted by Tayters View Post
    On older VRV's (talking 10yrs, R407C) have seen the expansions valves leaking on indoor and outdoor units. If the leak detector goes off inside the unit, assuming you can get in there well enough then unscrew the head then you can see bubbles with leak spray. Outdoor EEV's bit simpler to check.

    Not sure how this applies to newer models but thought worth a mention.

    Cheers,
    Andy.
    Thanks Andy - I'll keep that in mind.