    system without refrigerant



    Hey everyone,
    I am new here, I have question: how if we run system without refrigerant (the system has vacum).
    Is make compressor broken?



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: system without refrigerant

    Hi wutomo
    Welcome to the forum, If I can guess what your question is related too?

    Given the huge range of equipment and products discussed on the forum.
    The one type of compressor that you do not run in a vacuum is Hermetically sealed scroll compressor.
    Basically as far as I understand it and others feel free to correct me!

    If you apply a voltage to the motor windings when the compressor is in a vacuum.
    Then insulation of those motor windings are compromised and the motor is damaged.

    An alternate answer for bigger semi hermetic compressers which rely on suction gas flow across the motor to cool them. Can also be damaged when running in a vacuum.

    Large recips although capable of running in a vacuum could suffer from low oil pressure problems.

    Any system running in negative pressure unless designed to do so, could draw in air and that;s another set of issues.
    Sorry for not being to specific but it is difficult to second guess what your actual conditions where resulting in your implied failure!
    Grizzly

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: system without refrigerant

    If its a hermetic, scroll or semihermetic compressor the motor windings can be damaged by arcing if electrical power is supplied to the motor when there is a deep vacuum present.

    I expect an open drive compressor could suffer a mechanical failure from oil problems if run long enough in a vacuum.
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Feb 2015
    Location
    surabaya
    Posts
    3
    Rep Power
    0

    Re: system without refrigerant

    I mean: the system is air conditioning 1hp use hermatic compressor and there are oil for cooling it. ... is there oil flow when compressor running?

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: system without refrigerant

    Air-conditioning hermetic compressors are not cooled with oil. They are cooled with suction gases! Therefore if there is no refrigerant, there is no cooling of motor! Result is motor windings burning and mechanical damage, because oil is not circulating without refrigerant (oil is mixed and carried in system by refrigerant).

  6. #6
    Join Date
    Feb 2015
    Location
    surabaya
    Posts
    3
    Rep Power
    0

    Re: system without refrigerant

    ok, I know ... thank's a lot

  7. #7
    Join Date
    Feb 2015
    Location
    India
    Posts
    43
    Rep Power
    0

    Re: system without refrigerant

    The compressor, if system is in vacuum, would only get damaged after some time of running, if low suction pressure protection is present then the compressor would not start.