    Exclamation Reducing diameter of rising suction pipe for oil return



    Hello

    I am about to fit a domestic walk in dairy fridge set point 5c load about 1kw. Danfoss Optyma outside, Searle TEC Evaporator inside.

    Pipe run is about 25M and the outdoor is above the indoor by about 1M, similar to a cellar.

    Liquid 1/4 copper
    Suction 3/8 copper

    I have been advised by my supplier to reduce the suction for oil return to 1/4 where the pipework rises, this would be a couple of sections about 500mm.

    Can anyone explain the thinking behind this theory, I've never come across this before and I am unsure about reducing a 3/8 suction to 1/4.

    Thanks



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Reducing diameter of rising suction pipe for oil return

    I can see no reason to reduce from what is already a very small suction to 1/4. The reasoning would be incresed velocity to drive oil up the line but for a 500mm rise, bit overkill i think. I'd have gone 1/2 suction with a 3/8 liquid but depends on how small room is?
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Reducing diameter of rising suction pipe for oil return

    .

    Who is your supplier?

    Reducing the suction to 1/4" will create a pressure drop.
    If you are worried about oil return put a oil trap top and bottom
    of the riser.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Reducing diameter of rising suction pipe for oil return

    On 25 M run you will need to increase the diameter by two steps to maintain cooling and cooling the compressor.

    Suction to 5\8 and liquid to 3\8.

  5. #5
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Reducing diameter of rising suction pipe for oil return

    Hi
    This is all to do with oil return. The small hermetic compressors in these units have only a few cc's of oil in them and it is easy for them to run out of oil and seize up unless the pipe work is designed to assist the oil return. 25 metres of pipe run is a lot for a small black pot , so the suction pipe work exiting the evaporator should have a shallow trap in it so that once to oil has exited the evaporator it can't run back into the evaporator. Then the suction run from the short riser from the evaporator should have a slow in incline back to the compressor to assist the oil to naturally run back towards the compressor . During the system evacuation I would then draw a couple of cc's of extra oil into the system so that the system has a sufficient amount of oil to keep the compressors oil level constant ie the amount of oil leaving the compressor should equal the amount of oil returning to the compressor. Failure to add a small amount of oil to the system , and the compressor then running dry and seizing will lead to a warranty rejection of the seized compressor.

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Reducing diameter of rising suction pipe for oil return

    You can fit a small oil separator. 25M run is rather long for 1/4 and 3/8. Liquid line might not supply a full head to TX, or starve a capillary tube feed due to pressure drop. Definitely don't reduce suction to 1/4" on your riser.
    Last edited by mikeref; 02-11-2015 at 09:14 AM. Reason: Remember to proof read Mikeref :(
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Reducing diameter of rising suction pipe for oil return

    Thanks, but I can't say I'm any further forward. Would anyone else like to throw in a completely different and opposing view to all the others?

    It might be easier to have a fight.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Reducing diameter of rising suction pipe for oil return

    get the condensing unit much closer, 3m at the most and your problems are over.

  9. #9
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Reducing diameter of rising suction pipe for oil return

    Hi Contactor
    Send me your email address or speak to Joe or Ron at D&W Glasgow and ask for a copy of Glenn's WHY COMPRESSORS FAIL articles especially PART 5 this might help you in your probblem

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Reducing diameter of rising suction pipe for oil return

    Hi .Contactor
    google search " Saravel Refrigerant Pipe Sizing ", a useful program for selection pipe sizes.
    magoo