    Long vertical suction line dual risers



    Hi guys,

    can you please help us with calculating and selection of the suction line for the ice machine
    GRAM RIA 10.2? (Pump system - wet return line)
    Currently RIA 10.2 is connected without riser and it is located
    10 meters below main NH3 wet suction line of the system -45°C and
    the main suction line where RIA 10.2 is connected is 20 meters
    from vessel -45°C (10m vertical and 20m horizontal pipe).
    Liquid NH3 is supplied with TH-WITT pump HRP8050 from vessel -45°C (3:1).
    Our client is not always getting temperature of cold brine -40°C, instead they
    get temperatures of cold brine from -36°C to -40°C.

    I think that the main problem is incorrectly connected vertical suction line
    pipe DIN-EN 125 without riser (without botom and top P trap).

    In my opinion, for this case, RIA 10.2 suction pipe must be connected with dual risers
    because of vertical height of 10 meters and changable capacity.

    From ASHREA Refrigeration Handbook (SI) 1994 page 3.26, the velocity in the risers must be 25m/s or higher and on that fact Coolselector2 has selected pipe DIN-EN100 for 70% capacity and DIN-EN65 for 30% capacity.

    Are those pipes selected as it should be?
    Also attached are tehnical data for RIA 10.2 ice cream machine.


    Regards.
    Matija
    Attached Files Attached Files



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Long vertical suction line dual risers

    MatijaZGP,
    I'm not convinced you need a double riser, as they are for varying loads, do you have varying loads?
    Vertical riser might have to be in two steps with shallow traps, as well as if you do require double riser.
    Liquid feed in should be very carefully adjusted so as not to over feed to much to log suction riser.
    If brine pumps stops etc maybe interlock it to liquid solenoid.
    Oil could possibly cause some problems if floating around system , as it cannot return to suction line.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Long vertical suction line dual risers

    interesting read of specs, coil volume 610 litres, refrig charge 380 litres, confirm it is DX feed or pumped over feed. The riser should be designed for operating design velocities, and agree with Ranger oil logging in coil could be part of problem.

  4. #4
    Join Date
    Apr 2013
    Location
    Croatia
    Age
    34
    Posts
    12
    Rep Power
    0

    Re: Long vertical suction line dual risers

    I found shematic from GRAM itself for RIA 10.2 installed in Venezuela as you can see on attached photo. Sadly the vertical high is not written.
    Oil is blown to wet suction line when defrost starts, as you can see on the schema.
    The RIA 10.2 in my case is connected the same as on this schema, but without dual risers and
    P traps top and botom, and the suction pipe is DIN-EN125.
    Mostly this RIA operates at full capacity which is 28000 ice cream sticks per hour, but sometimes they slow down do 20000 or 16000 sticks/h, all depends of ice cream type.

    Also I have attached technical data for all GRAM RIA ice machines if someone needs it.
    Attached Images Attached Images

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Long vertical suction line dual risers

    Hi
    the pipe schematic is hard to read or understand, repeat as a pdf if you can.
    A single riser should be ok if expansion vavs are set up correctly, you should have a couple of degrees super heat at coil exit to ensure coil is not totally flooded and you get high velocity vapour all be it super saturated back to surge vessel.

  6. #6
    Join Date
    Apr 2013
    Location
    Croatia
    Age
    34
    Posts
    12
    Rep Power
    0

    Re: Long vertical suction line dual risers

    Here are the better photos.
    If you can't read the top three main pipes from top to botom one
    goes like this: 1. Hot gas, 2. Suction and 3. Liquid.
    Attached Images Attached Images

  7. #7
    Join Date
    Apr 2013
    Location
    Croatia
    Age
    34
    Posts
    12
    Rep Power
    0

    Re: Long vertical suction line dual risers

    Update dual risers:

    Today RIA 10.2 was put in operation and is working very good.
    Before when there was no dual risers they got brine temperature -36°C
    and now they have -39°C...-41°C.
    The temperature of inlet liquid ammonia is -44°C.

    Here is before and after picture of the top P-traps:

    Before.jpg After.jpg
    Last edited by matijaZGB; 01-02-2016 at 10:10 AM.

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Long vertical suction line dual risers

    Quote Originally Posted by matijaZGB View Post
    Update dual risers:

    Today RIA 10.2 was put in operation and is working very good.
    Before when there was no dual risers they got brine temperature -36°C
    and now they have -39°C...-41°C.
    The temperature of inlet liquid ammonia is -44°C.

    Here is before and after picture of the top P-traps:

    Attachment 13979Attachment 13978
    Thanks for the update, are you completely happy with result & fine tuning?

    I wonder what Gram would supply new today with latest designs, surely it's better!
    Last edited by RANGER1; 30-01-2016 at 11:55 PM.

  9. #9
    Join Date
    Apr 2013
    Location
    Croatia
    Age
    34
    Posts
    12
    Rep Power
    0

    Re: Long vertical suction line dual risers

    Yes, we are very happy with the result. (It's important that client is happy also )

  10. #10
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Long vertical suction line dual risers

    have you find why it happened?

    what was your suction pipe size before ? what is Now ?

    if your suction pipe size is small , you have more pressure in evaporator than your suction line therefor you have less temp. or if your liquid flow to evaporator more than your evaporator capacity it give you same result as small suction pipe size ,
    in these type of system it is better to put gags between evap. and main suction line.