    Exclamation Mitsubishi Heavy industries Duct type leak



    Hi i have a leak on an FDU250VD MIHI indoor
    the water is jumping out of the water pan towards the fans and then inside the duct.
    The evaporator is clean, i have installed a drain water trap without any results (MIHI says in the manual that a trap is not needed),the drain pan is clean, the drain pipe is ok,
    If i open the bottom sheetmetal on the unit while operating in cooling i can actually see the water jumping outside the pan. I took the unit apart to see what is wrong and i found that the insulation strip between the evaporator and the drain pan was damaged so i replaced it but the water still jumps out of the pan.
    I am an experienced engineer and these kind of problems usually get fixed with a proper drain trap.
    I was thinking that the evaporator is icing and i left it on fan only and tested it by pouring water in the drain pan.The water was still jumping out of the pan.
    It is an inverter unit so i shouldn't be worried about the coil temp being too low.
    Other engineers try to fix it before me with no results.
    The evaporator looks like its touching the drain pan correctly.
    Please help me on this one,
    Thanks!



  2. #2
    Join Date
    Dec 2010
    Location
    devon
    Age
    52
    Posts
    837
    Rep Power
    24

    Re: Mitsubishi Heavy industries Duct type leak

    Is return air restricted causing a part vacuum and pulling water into airflow

  3. #3
    Join Date
    Apr 2011
    Location
    Cyprus
    Age
    38
    Posts
    7
    Rep Power
    0

    Re: Mitsubishi Heavy industries Duct type leak

    no the return is open just a synthetic-foam clean filter
    the only thing i can think of is the evaporator being dirty from the insight it is a thick evaporator witch i cleaned with condenser clearer because it was very dirty
    the airflow seems fine on the outlets so i am confused

  4. #4
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    745
    Rep Power
    25

    Re: Mitsubishi Heavy industries Duct type leak

    I have exactly the same problem on a 25kw daikin system ?? No idea what is wrong with it ��
    My train of thought was that there was too much pressure being developed by the fan for the installed ductwork.

    Eggs

  5. #5
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: Mitsubishi Heavy industries Duct type leak

    Hi Christos
    Have you tried running without the return air filter in to see if the problem still exists?
    Is the return air duct too small for the volume of air being moved by the fan causing a low pressure?
    Paul
    Born to fish, forced to work

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Mitsubishi Heavy industries Duct type leak

    Face velocity too high, blowing water off the coil. Increase static by fitting a suitable return air filter which will reduce flow and face velocity.

  7. #7
    Join Date
    Mar 2010
    Location
    Indonesia
    Posts
    6
    Rep Power
    0

    Re: Mitsubishi Heavy industries Duct type leak

    Hi,
    Agree with Magoo, face velocity exceed 2.5 m/s, water from coil carry over.

    Try to reduce the speed of motor or try to adjust the return grilles.


    IW

  8. #8
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Mitsubishi Heavy industries Duct type leak

    is there a bend in the supply duct close to the unit

  9. #9
    Join Date
    Dec 2010
    Location
    devon
    Age
    52
    Posts
    837
    Rep Power
    24

    Re: Mitsubishi Heavy industries Duct type leak

    On the ducted system u can adjust the velocity of evap fans depending on number of ducts size and bends I remember doing it on a mhi course you can go in controller and reduce speed not just hi or low speed actuall rpm of motor

  10. #10
    Join Date
    Apr 2011
    Location
    Cyprus
    Age
    38
    Posts
    7
    Rep Power
    0

    Re: Mitsubishi Heavy industries Duct type leak

    there is no return duct, is just the unit with a new clean synthetic filter. I tested the unit without the filter and it does the same thing. Customer claims that the unit was working for 4 years without any problems.
    The only two things i suspect is the evaporator itself being dirty from the insight or the evaporator getting too cold due to faulty liquid line-suction sensors.
    i will test it on low speed as well to see if that stops the water form jumping out of the tray.
    Those MiHI units are really cheap quality, the frame that holds the evaporator is rusted and maybe the evaporator is not in the right place or angle. It says made in PRC.

  11. #11
    Join Date
    Mar 2010
    Location
    Indonesia
    Posts
    6
    Rep Power
    0

    Re: Mitsubishi Heavy industries Duct type leak

    If it has been running well for 4 years, than it has nothing to do with fan speed.
    You have to make sure the water is from coils or from drain pan first.

  12. #12
    Join Date
    Apr 2011
    Location
    Cyprus
    Age
    38
    Posts
    7
    Rep Power
    0

    Re: Mitsubishi Heavy industries Duct type leak

    while the unit was running i half opened the bottom-sheetmetal and with my torch i saw the water jumping out of the pan towards the fans
    nobody had this problem with MIHI before? please reply

  13. #13
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Mitsubishi Heavy industries Duct type leak

    of course it will by taking access cover off, you increase fan flow rate.

  14. #14
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: Mitsubishi Heavy industries Duct type leak

    Hi Christos
    You have said the water is jumping out of the pan towards the fan.
    Why is there that much water in the drain?
    If understand you correctly and the water is jumping out of the pan as droplets is there a lot of vibration when the fans are running?
    Paul
    Born to fish, forced to work

  15. #15
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Mitsubishi Heavy industries Duct type leak

    Check your condensate drainage. You should not have that amount of standing water in the pan if the drain is correctly trapped and has the correct fall.

    When you switch the unit off, does the drain pan empty?

  16. #16
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    745
    Rep Power
    25

    Re: Mitsubishi Heavy industries Duct type leak

    Frank, what do you call correctly trapped?
    On my system I have tried no trap, standard trap and inverted p trap. It still fires water down the duct and it drips out about 2m away from the fcu.

    My system also runs with no return air duct. Before I give up and flog 'em a new 'un, I still need to try a thicker filter with more resistance to see if that helps.

    Cheers

  17. #17
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Mitsubishi Heavy industries Duct type leak

    eggs,
    water trap has to have water head what ever that exceeds, the suck factor of fan expressed in inches of water head. Best to fit a clear plastic tube in a circular loop and watch what the water is doing, if bouncing around no water will drain, add inches for a stable water level in trap.
    With no return air ducting and just a filter the fan static drop so fan will over perform , either add balance louvers or double filter resistance. Either that or select a lower fan speed and gauge performance. If you have an anemometer get flow velocity average across filter multiply by area and get flow rate , check against AHU design and adjust accordingly.
    Last edited by Magoo; 23-10-2015 at 02:40 AM.

  18. #18
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Mitsubishi Heavy industries Duct type leak

    Each fan create some vacuum between evaporator and fan. if air filter or evaporator is dirty, vacuum will be greater. To drain condensate from vacuum space, water column in the trap should be greater than vacuum. In your case trap can be undersized. Increase height (distance from bottom of the pan to bottom of the trap) of the trap. Water should not stand in the pan and pan should be sloped to the drain.

  19. #19
    Join Date
    Apr 2011
    Location
    Cyprus
    Age
    38
    Posts
    7
    Rep Power
    0

    Re: Mitsubishi Heavy industries Duct type leak

    Thanks for all your help. I tried everything and nothing works, the trap is small but i cannot put anything bigger since the unit is on low level ceiling in a Gym and there is no space for a bigger trap.
    The space is very humid and i think the evaporator is dirty from the insight, it looks clean on both sides but it is very thick and i think dirt is stack in the middle.I washed it 3 times even with condenser chemical and i can still see dirt coming out.I think the air restriction caused by the evaporator is why i get water in the duct.
    I said to the owner that he needs a new unit, i spend a lot of hours trying to fix this issue. I advised the owner to use a unit with an internal water pump. Again thanks for your help!

  20. #20
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Mitsubishi Heavy industries Duct type leak

    Now you tell us system is in a gym.
    With new system add lots of fresh air and extract as well. If coil core is blocked beyond recovery it is all the skin and body particules that over heated bodies express and lack of suitable filtration initially.

  21. #21
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Mitsubishi Heavy industries Duct type leak

    Quote Originally Posted by Christos View Post
    Thanks for all your help. I tried everything and nothing works, the trap is small but i cannot put anything bigger since the unit is on low level ceiling in a Gym and there is no space for a bigger trap.
    The space is very humid and i think the evaporator is dirty from the insight, it looks clean on both sides but it is very thick and i think dirt is stack in the middle.I washed it 3 times even with condenser chemical and i can still see dirt coming out.I think the air restriction caused by the evaporator is why i get water in the duct.
    I said to the owner that he needs a new unit, i spend a lot of hours trying to fix this issue. I advised the owner to use a unit with an internal water pump. Again thanks for your help!
    You can use condensate pump.

  22. #22
    Join Date
    Apr 2011
    Location
    Cyprus
    Age
    38
    Posts
    7
    Rep Power
    0

    Re: Mitsubishi Heavy industries Duct type leak

    the reason i recommend a unit with internal pump is that those systems don't require any traps and usually the fans are blowing on the evaporator instead of sucking the air.